After carrying out a PIR on a domestic property do you have to label up the consumer unit with the appropriate stickers, such as the date of next inspection.?

and

if any stickers are not there i.e rcd stickers, is it upto the inspector to place them on the board?

cheers
 
You are inspecting the job, the whole idea being you report to the client your findings whether it is wrong circuit breakers or labeling. You produce your PIR for the client, put a sticker on the board as to the date and a recommendation as to when the next inspection is carried out.

Now, obviously it depends on what you find as to what gets done, obviously if you find some number ones then probably something needs sorting out to make it safe.
 
All you have to do pal is put a sticker on saying the date of the last inspection and a recommended date for the next inspection you probably no which ones i mean no other labelling has to be done although if their is none this should be noted on your oberservations and recommendations page as you are only doing a report.:D
 
Many thanks everyone that was a great help.:)

Im actually a construction manager who used to have an electrical business being self-employed. Im in the process of setting up a inspection business doing a few jobs whilst keeping my current job. Do you know if there is much call for this work?
 
Last edited by a moderator:
Many thanks everyone that was a great help.:)

Im actually a construction manager who used to have an electrical business being self-employed. Im in the process of setting up a inspection business doing a few jobs whilst keeping my current job. Do you know if there is much call for this work?

Probably depends which part of the country you are in
 

Reply to PIR Labels in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all. I have a small question about inspection interval labels. We all know to fit one of these labels with the relevant date upon completion of...
Replies
10
Views
805
Hi All, I am in the middle of purchasing a small 1 bed flat in England, and have been sent a Domestic Electrical Installation Certificate by the...
Replies
1
Views
1K
I've recently has an EICR (report attached) carried out on my two bed flat because I need to rent it out for a year. The electrician has come back...
Replies
19
Views
893
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
604

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock