Discuss Pir light in the Australia area at ElectriciansForums.net

D

ds1980

Am trying to wire outside light. Switch is inside 2 gang 2 way. Fuse trips if I wire switch and permanent feed but is fine if I don't add live wire from switch? However I then can't turn it on and off as such although still works as pir? Any help appreciated. Ta
 
you need to use your switch as an override. i.e. put the switch across the permanent live and the switched live on the PIR
 
great thank you but i cant run any more cables?? i have 2 x brown, blue and earths going into back of pir light. one is the feed from last light on the circuit and one goes from switch to light. live neutral and earth connections in the back of the pir light. can i still sort this?
 
Sounds to me like you are connecting both browns and blues together in the light....when you switch on the overide switch you are effectively causing a dead short.....apologies if I have got this wrong.....if I have got it right I would question your competance to be carrying out electrical work safely.
 
agree with wirepuller. it's all well and good to do the odd diy job around the house, but if you have not got the right equipment and knowledge to do the job, you should call in an expert. i need a new brain, but think it's better to employ a brain surgeon than try and do it myself with a stanley knife and hacksaw
 
you only need a permanent live, switched live, n and earth. live into the common and sw live into L1. bell out the wires, as long as you know which core is which you shouldn't have any bother.
 

Reply to Pir light in the Australia area at ElectriciansForums.net

Similar Threads

Hi, Heavy industrial spark here, never do house bashing hence the question. I currently have a light switch at the front door not doing anything...
Replies
1
Views
442
Hi there, I have an outside light that is turned on with a switch from inside and would like to change it to a PIR version incorporating an...
Replies
8
Views
1K
Hi, I’m looking to install 3 meross smart switches for 3 lights: entrance switch: only 1 gang but 3 way switch bedroom switch: 2 gang (1 is 1...
Replies
9
Views
363
Hi I want to add a light to my attic. There is a single switch on the landing that I want to change to a double switch and then use it to still...
Replies
24
Views
1K
Hi, I have a single light switch, wired like this.. the 2 wires in com, with a always live wire coming to the switch, and then wire going out to...
Replies
6
Views
686

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock