Discuss pir questions in the Australia area at ElectriciansForums.net

D

dochisholm

ok my first pir is going ok. COuple of questions to finish ot up firstly there was no earth at a metal light in the lounge as it was twin with no earth replaced for insulated pendant ok for a code 4 now?. The downlights in the upstairs hall are class 2 rated with no earth running to them on twin cable code 4?. finally in writing up my report i have put testing or only accesbile sockets. This incorporates drops to appliances under worktops is this an acceptable term for limitation or should i clarify also any sockets i could not access due to furniture e.t.c
 
sounds ok to me. remember to label the CU as no cpc on lighting, use class 2 fittings only. might give it a code 2, as requiring improvement. see what othewrs say.
 
yep code 2, and code 4 it, the more comments the better right?, you should also mention all the accessories you could not access, ie known socket in living room, behind furniture inaccessible.
More writing, but makes the report look good. :)
 
there is cpc on lighting just a jb above ceiling to this one metal light in lounge with only twin to it. and the downlights have a jb with short length on twin to the back of the lights which are class 2
 
i'd mark it down as incomplete/missing cpc's and give it a code 2. alternatively. repair the fault from the JBs ( chargeable of course ) then you can give it a satisfactory after testing.
 
Have you looked at the guide IQ? Just checked the other thread where MrEnigma reckons code 2 doesn't warrent an unsatisfactory assessment. IMO he is incorrect and quote from the guide as follows.
Page 10 "It would not be reasonable to indicate a "satisfactory" assessment if any observation in the report had been given a code 1 or code 2 recommendation"
 
I know the guide like the back of my hand, that paragraph is actually highlighted.

It's just frightening that someone could be producing 'satisfactory' PIR's with code 2 defects listed!
 
Have you looked at the guide IQ? Just checked the other thread where MrEnigma reckons code 2 doesn't warrent an unsatisfactory assessment. IMO he is incorrect and quote from the guide as follows.
Page 10 "It would not be reasonable to indicate a "satisfactory" assessment if any observation in the report had been given a code 1 or code 2 recommendation"

hardly conclusive
 
Can he back up his opinion with facts?
Any regs or accepted advice/guidance would be good. I'm with you IQ.
Sorry should have put "lol" after asking if you'd checked the guide, it was said with my tongue firmly in my cheek.
 
I recently done a PIR that consisted of 70 DB's fed via 2 400 Amp 3 phase sub mains, any code 1 issues had to dealt with immediately, as the client wanted a satisfactory report. (as agreed by all the client engineers) After the report was submitted, an order was then placed to rectify all the code 2's.
This was done for a London Borough Council
 
Can he back up his opinion with facts?
Any regs or accepted advice/guidance would be good. I'm with you IQ.
Sorry should have put "lol" after asking if you'd checked the guide, it was said with my tongue firmly in my cheek.

You're right sjm, it's a fast-track way to losing respect and trust on a forum.

I just hope anyone learning the ropes reads the whole thread and comes to the right conclusion.
 
Last edited:
I recently done a PIR that consisted of 70 DB's fed via 2 400 Amp 3 phase sub mains, any code 1 issues had to dealt with immediately, as the client wanted a satisfactory report. (as agreed by all the client engineers) After the report was submitted, an order was then placed to rectify all the code 2's.
This was done for a London Borough Council

Ah well that is conclusive, makes my industry-wide approved guide look rather silly now....
 
If you can show me some hard evidence that ALL code 2's are unsatisfactory I will gladly accept the fact, and indeed go back to the engineers of that council, and shove it where the sun dont shine. I am just a doer, they are the engineers.
 
It's a fast-track way to losing respect and trust on a forum.

I just hope anyone learning the ropes reads the whole thread and comes to the right conclusion.

Sorry IQ can't quite work this out, is it aimed at me?

Edit: Long day, wrong end of stick.
 
Last edited by a moderator:
If you can show me some hard evidence that ALL code 2's are unsatisfactory I will gladly accept the fact, and indeed go back to the engineers of that council, and shove it where the sun dont shine. I am just a doer, they are the engineers.

What is the meaning as per BS7671:2008 of a 'code 2 defect' ?

Answer: Requires improvement

If something requires improvement, is it then satisfactory for continued service?

Read the list of code 2 defects in the guide that you already have and tell me which ones you'd be happy to ignore, bearing in mind that once you issue a 'satisfactory' report, no further defects are likely to be rectified!

If you still can't man up and admit error for the sake of this thread and anyone learning the ropes, I give up.
 
I recently done a PIR that consisted of 70 DB's fed via 2 400 Amp 3 phase sub mains, any code 1 issues had to dealt with immediately, as the client wanted a satisfactory report. (as agreed by all the client engineers) After the report was submitted, an order was then placed to rectify all the code 2's.
This was done for a London Borough Council

Isn't this the correct procedure??
Code 1's require immediate action and code 2's require remedial action as soon as possible in order to rectify a potential danger.
With this in mind how can an installation with code 2's be classed as satisfactory.
I think that the fact that "an order was then placed to rctify all the code 2's" speaks volumes don't you!
 

Reply to pir questions in the Australia area at ElectriciansForums.net

Similar Threads

Hello, I am renovating a house. I am rewiring myself. I am getting an electrician to install a new consumer unit & test all my work. I'm looking...
Replies
20
Views
3K
Hi all, first post so go easy! This is for people who are looking for more info on the course and exams and is from my experience of doing the...
Replies
1
Views
3K
I realise this overlaps with the Earth Rod install post a little, but I am attempting to plan part one of an upgrade. Currently I am mostly...
Replies
24
Views
6K
Hi. This is a gloriously messy installation I looked at this morning at a house a friend just purchased. It t became quickly clear it was more...
Replies
7
Views
1K
I do seem to pick only the weirdest properties to inspect... Victorian terraced house today - with up front RCD to a Wylex fuse board and main...
Replies
24
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock