I've just been told by our local authority that we need planning permission for any agricultural/commercial buildings, that it doesn't come under permitted development. Has anyone else come accross this????
Discuss Planning Permission for Commercial Roofs in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net
what this mean is that as MCS Certified we are 'Competent Persons' - this applies to both the electrical (Part P stuff) and the Structural Calcs.I can confirm that a building regulation application is not required for Solar PV Panels if the person carrying out the installation is registered with a Competent Person Scheme as detailed in row 17 of Schedule 3 of the Building Regulations 2010. It has been interpreted that under Row 20, the installer is responsible for ensuring compliance with Part A.
Our NAPIT assessor insisted that a visual inspection was inadequate."4.4.4 The contractor shall ensure that the roof structure is capable of withstanding the loads (static and wind loads) that will be imposed by the PV modules and their mounting arrangements. If there is any doubt, a structural engineer must be consulted."
Other than in Scotland, where a new law comes into force on 18th March, all non-domestic buildings in England and Wales require planning permission for microgeneration.
The current permitted development here only applies to dwellings.
There was a consultation on bringing in permitted development for commercial buildings in England and Wales but it hasn't materialised yet.
Ok, so I've looked at this again, thanks to TedM - as I see it I'm planning to install 9.8kwp on a garage that is within the curtilage of the property, the pv isn't not going to be used for commercial reasons, no vat being reclaimed, not offset against any allowances all claims against domestic use in an off gas grid house. I reckon it comes under permitted development. What do other peeps think???
Reply to Planning Permission for Commercial Roofs in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net