Can anyone point me to reg that says about plastic boards under stairs or does one not exist

On an EICR and they have a plastic baord under the stairs.. C2 or C3?
 
421.1.201 deals with consumer units in domestic installations.
The regulation mentions nothing about location, however a risk assessment of the location of an existing plastic CU may lead the inspector to adding a code based on for instance , if it’s in a sole escape route or under a staircase where a fire could increase the risk of danger for escape or entry for say rescue.
Id personally never C2 any plastic CU based on material alone.
 
There is no reg stating anything like that - the usual convention is:
No signs of damage - no comment
No signs of damage and in an escape route or under a combustible escape route - C3
Signs of thermal damage - C2/FI/C1 depending upon the condition - usually C2
 
I’d personally always comment if the CU doesn’t comply with the current regulations in the additional notes section , however I would not code it on the grounds of being simply plastic and say located near a front door but there’s rear access to the property etc.
 
'CU in a domestic household premises is not metal or installed in a non-combustable cabinet, showing NO signs of thermal damage, located in the sole means of escape for a dwelling are'

Reg 421.1.201

C3
 
'CU in a domestic household premises is not metal or installed in a non-combustable cabinet, showing NO signs of thermal damage, located in the sole means of escape for a dwelling are'

Reg 421.1.201

C3
The regulation doesn’t say that, it mentions no location.
The location is commented on in the BPG 4 only which I think is what you have quoted?
 
The regulation doesn’t say that, it mentions no location.
The location is commented on in the BPG 4 only which I think is what you have quoted?
I quoted The Napit guide which lists the Reg they consider relevant. But, yes BPG also.

Either way a C3 for me under those specific circumstances
 
Personally (assuming that it's in good condition and I have no reason to believe that the plastic has failed to meet non-combustibility requirements of BS EN 60439-3/BS EN 61439-3) I always give a C3 observation, regardless of whether it's located within the sole escape route or not.
 

Reply to Plastic boards under stairs in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Doing some work in a commercial restaurant/kitchen the builders had already boarded and plastered the walls meaning my only viable route is to use...
Replies
31
Views
1K
Quick question. I want to put an isolating 2p switch on my incoming supply from the meter to the board. I want this to allow easier board changes...
Replies
8
Views
832
I know once you see plastic entering then you don’t need to bond as it says on site guide.(enters the house plastic then it’s metal) Would I be...
Replies
14
Views
2K
When doing an eic, does anyone put limitations for existing wiring within walls and under floors and you’re not able to check them? Or what do...
Replies
5
Views
956
Was having a poke around the old man's house today. Anyway. DB is under stairs (18th ed following a recent extension. Not done by me but it's...
Replies
7
Views
718

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock