Hi fellas,

I was wondering if somebody could help me with a wiring diagram please, it is an existing system that has had underfloor heating added.

The system is:

Oil fired fully pumped system ie

motorised valve on heating
motorised valve on the dhw


Addition:

Underfloor heating manifold with motorised valve
pump


Basically I want to be able to switch the underfloor heating on independently, but the problem is the second pump on the underfloor heating.

Thanks In Advance
Acestu
 
Re: Please Help with Wiring Diagram !I was wondering if somebody could help me with a

The last time I did this was as described;

The underfloor stat (and timed control if fitted) calls for the floor pump.
A pipe stat on the U/Floor flow calls for the motorised valve when temp drops.
The motorised valve aux switch calls for the boiler, which normally has control of the main pump.

The underfloor flow should have been piped off the boiler flow before the heating motorised valve, then the floor heating can be controlled independently of the main heating.
If it hasn't been, the floor motorised valve will have to call for the main heating.
 
Last edited:
Re: Please Help with Wiring Diagram !I was wondering if somebody could help me with a

The last time I did this was as described;

The underfloor stat (and timed control if fitted) calls for the floor pump.
A pipe stat on the U/Floor flow calls for the motorised valve when temp drops.
The motorised valve aux switch calls for the boiler, which normally has control of the main pump.

The underfloor flow should have been piped off the boiler flow before the heating motorised valve, then the floor heating can be controlled independently of the main heating.
If it hasn't been, the floor motorised valve will have to call for the main heating.


Hi Snowhead,

Yes it is all piped separately from the other side of the oil fired boiler.

Thanks for the reply but this would not work because as soon as you call for the boiler it switches on both the boiler and the main ch & dhw pump as they are wired together, ( I think that explanation sort of simplifies my problem ).

Cheers anyway

Acestu
 
Re: Please Help with Wiring Diagram !I was wondering if somebody could help me with a

Thanks for the reply but this would not work because as soon as you call for the boiler it switches on both the boiler and the main ch & dhw pump as they are wired together, ( I think that explanation sort of simplifies my problem ).

Cheers anyway

Acestu


That's how it needs to be.
The Under floor pump circulates around the floor.
The main pump circulates around the boiler and floor header circuit.
The underflor pump won't (most likely won't) circulate around the boiler
 
Re: Please Help with Wiring Diagram !I was wondering if somebody could help me with a

That's how it needs to be.
The Under floor pump circulates around the floor.
The main pump circulates around the boiler and floor header circuit.
The underflor pump won't (most likely won't) circulate around the boiler

Hi Snowhead,


The flow on the boiler goes into a pump and then to a manifold with a 2 port valve for the DHW and a 2 port valve for the Heating, so if the underfloor heating calls the boiler it switches the boiler and the pump of the main system, that means that the pump is pumping against 2 closed motorised valves, I need the Under floor heating to switch on just the boiler of the main system and its own pump.

Thanks Again
Acestu
 
Re: Please Help with Wiring Diagram !I was wondering if somebody could help me with a

Hi Snowhead,


so if the underfloor heating calls the boiler it switches the boiler and the pump of the main system, that means that the pump is pumping against 2 closed motorised valves, I need the Under floor heating to switch on just the boiler of the main system and its own pump.

Thanks Again
Acestu

I'll give up after this post.

Is the floor circuit not connected between the pump and the manifold? As there is a manifold it should be on that, without a valve.

It doesn't matter about the closed valves.
The loop to the floor circuit will be open, the floor circuit pump won't pump around the boiler circuit.

.
 
Last edited:
Re: Please Help with Wiring Diagram !I was wondering if somebody could help me with a

I'll give up after this post.

Is the floor circuit not connected between the pump and the manifold? As there is a manifold it should be on that, without a valve.

It doesn't matter about the closed valves.
The loop to the floor circuit will be open, the floor circuit pump won't pump around the boiler circuit.

.

No, the underfloor equipment is completely on the other side of the boiler ie on the left there is a flow and return that is used for the main system that I installed some years ago.

Then a builder came along and used the right hand side of the boiler, another flow and return to add the under floor heating which has its own pump and motorised valve.

Hope this explains it better.

cheers
Acestu
 
Re: Please Help with Wiring Diagram !I was wondering if somebody could help me with a

In light of the additional missing information, you need to move the underfloor flow pipe from the boiler to the existing manifold or between the pump and manifold. The underfloor return can stay in the boiler. Then follow the plan above.

The underfloor system has it's own pump and valve so as to control and reduce the temperature of water flowing around the floor pipework. You don't pump directly around the floor and boiler, the floor temperature will get too high.
 
Re: Please Help with Wiring Diagram !I was wondering if somebody could help me with a

In light of the additional missing information, you need to move the underfloor flow pipe from the boiler to the existing manifold or between the pump and manifold. The underfloor return can stay in the boiler. Then follow the plan above.

The underfloor system has it's own pump and valve so as to control and reduce the temperature of water flowing around the floor pipework. You don't pump directly around the floor and boiler, the floor temperature will get too high.

Hi, I realise that I can do what you are saying, but it is a great deal of work because the said builder built a kitchen around all the existing pipework, which is why I am trying this electrically because I can just about get to this. The underfloor unit has a temp controlled bypass on it so that it does not get too hot.

thanks for bearing with me
Acestu
 
Re: Please Help with Wiring Diagram !I was wondering if somebody could help me with a

The underfloor unit has a temp controlled bypass on it so that it does not get too hot.

Acestu

That's a relief, I thought you were going to pop up and say it's flow from boiler thro' floor pump, thro floor pipe, back thro return to boiler.


O.K, so Oil fired, cast iron heat exchanger if it's 4 hole, hopefully the boiler doesn't have control of the main pump for run on after burner off.
Your existing controls call for the pump and boiler at the same time?

Where is the floor pump fitted;
In the flow from boiler to floor manifold?
or in/on the manifold?

Any motorised valve between the boiler and manifold?


Mechanical (bulb) thermostat controlling bypass valve strapped to the pipe?
 
Last edited:
Re: Please Help with Wiring Diagram !I was wondering if somebody could help me with a

In light of the additional missing information, you need to move the underfloor flow pipe from the boiler to the existing manifold or between the pump and manifold. The underfloor return can stay in the boiler. Then follow the plan above.

The underfloor system has it's own pump and valve so as to control and reduce the temperature of water flowing around the floor pipework. You don't pump directly around the floor and boiler, the floor temperature will get too high.


I can't get to that side of the boiler to move any pipework, because it has had a kitchen built around it, but I can get to the electrics which is why I am asking for a diagram to do it electrically.

I think I will just build a logic switching unit myself, as it doesn't seem as if there are any available commercially.

thanks
Acestu
 
Re: Please Help with Wiring Diagram !I was wondering if somebody could help me with a

I think I will just build a logic switching unit myself, as it doesn't seem as if there are any available commercially.

thanks
Acestu

You don't need anything complex, at worst a relay some connectors and box to put them in and a (programable ) thermostat to control the floor.

There's allsorts of commercial controllers
 
Re: Please Help with Wiring Diagram !I was wondering if somebody could help me with a

You don't need anything complex, at worst a relay some connectors and box to put them in and a (programable ) thermostat to control the floor.

There's allsorts of commercial controllers


Hi Snowhead,

Yes I realise that, that's what I was asking, I just can,t seem to find anything on the internet ie a diagram or relay unit, I suppose I need something like the old smc controller that had 2 separately switched pumps and boiler switch.

cheers
Acestu
 
Re: Please Help with Wiring Diagram !I was wondering if somebody could help me with a

OK, I have sussed it, just put this diagram together with a dpdt 230 volt relay, I am posting a link to the diagram just in case anybody else needs it....

Zippyshare.com - solution.jpg

cheers
Acestu
 
Re: Please Help with Wiring Diagram !I was wondering if somebody could help me with a

The only problem I can see is the DHW and/or Main heating will take priority over the floor heating.

.
 
Re: Please Help with Wiring Diagram !I was wondering if somebody could help me with a

Hi Snowhead, can you explain a bit more please..

thanks
Acestu
 
Re: Please Help with Wiring Diagram !I was wondering if somebody could help me with a

OOPs, missed where the floor pump is connected.
Thought the relay changing over would isolate the floor pump, but that only needs the floor circuit to call to feed the pump, the boiler is already on.
 
Re: Please Help with Wiring Diagram !I was wondering if somebody could help me with a

So you think this should be ok then ?

thanks
Acestu
 

Reply to Please Help with Wiring Diagram !I was wondering if somebody could help me with a wir in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

Up until now I have steered clear of heating systems. I now have quite a bit of work with a builder and will be expected to deal with the...
Replies
4
Views
865
I've pretty much sussed out the wiring for the radiators and underfloor heating, thanks to help from the forum. I do have one more question...
Replies
6
Views
684
I have not had to do the wiring for a wet underfloor heating system before. I think I started a thread fairly recently and had some very good...
Replies
24
Views
2K
A nice easy one for all the (many) people that are cleverer than me 🙂. Could you please point me in the direction of a wiring diagram for a...
Replies
1
Views
925
Hello Guys, I was wondering if any of you nice chaps could lend me some advice. So I have an open vented heating system with a 3 port valve...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock