Discuss PME on a farm?........... in the UK Electrical Forum area at ElectriciansForums.net

HappyHippyDad

-
Esteemed
Arms
Reaction score
5,607
I am about to install 4 sockets in 4 separate stone enclosures, housed within a large stone outbuilding. They have stone floors and are completely weatherproofed. They may be having small animals in them, goats, sheep etc.

The existing set up is TN-C-S.

BS7671 doesn't go into much depth with regards earthing. 705.411.4 just says a TN-C system shall not be used. Does this mean just TN-C, or does it also mean TN-C-S? It's a little confusing as the title to this regulation is TN system.

Is the thinking that there may be some potential between the PME earth and actual earth and that this potential could become lethal to livestock? Is this more likely in muddy, wet, earth floored barns or is it just as relevant in my situation above (all stone).

The existing electrical system has been very well installed, which leads me to think this has been thought out, as it must have been installed whilst this regulation was in practise...... making me think perhaps it doesn't need a TT for some reason. Here is a picture of the supply...

3 phase supply.jpg
 
Thought that picture was familiar:

 
The note, just below this reg, says "This does not preclude the use of TN-C-S."
Just realised I was looking in the Big blue, not the Big brown.
So this suggests it may be ok to use PME.
However, they recommend at earth grid is laid.
So really, TN-C-S is not going to be used if all the ground work is already laid?
 
Thought that picture was familiar:

It is rather nice to look at though 😀

I don't know what it is about it, but it makes me feel calm.
 

Reply to PME on a farm?........... in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

This thread is in relation to the job at the farm I am thinking of taking on (3 phase thread). At present the farm is all PME. I believe it needs...
Replies
9
Views
2K
I've been installing Type 2 SPDs in consumer units for several years now, and they always come as a pair, connected across L & E, and across N &...
Replies
2
Views
523
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
532
Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Replies
6
Views
2K
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock