This thread is in relation to the job at the farm I am thinking of taking on (3 phase thread).
At present the farm is all PME. I believe it needs to be TT'd as they have now brought 2 x goats in to the main barn (no other animals anywhere). In addition they have some feed for the goats and also some plants may be grown in there. The barn is all stone flooring. I will never be able to confirm if it has a metal grid underneath so I have to assume it doesn't.
Looking at 705.411.4, the note states a TN -C system shall not be used, but a TN-C-S system is not precluded.
705.415.2.1 says that PME is not 'recommended' unless a metal grid is installed.
Now, I have discussed the word recommended with Napit and also the IET and they say it basically means it is up to the installer. It is not mandatory. However, I would have to justify why I have chosen not to use the recommendation.
2 goats, a few sacks of feed and a few plants in a massive (metal) barn (approx 75m x 25m).
What is the actual risk of sticking with the PME? Is it the potential between true earth and the PME earth. The barn will be bonded so it will be at PME earth. The ground will be at actual earth, so is the problem if the goat brushes against the metal barn whilst standing on the ground and there is a potential difference. Or, is it more to do with fault conditions?
Is this an obvious case of needing a TT, or perhaps not so obvious?
I know I have discussed this before, but now it is becoming a reality I thought I would discuss it again/further.
At present the farm is all PME. I believe it needs to be TT'd as they have now brought 2 x goats in to the main barn (no other animals anywhere). In addition they have some feed for the goats and also some plants may be grown in there. The barn is all stone flooring. I will never be able to confirm if it has a metal grid underneath so I have to assume it doesn't.
Looking at 705.411.4, the note states a TN -C system shall not be used, but a TN-C-S system is not precluded.
705.415.2.1 says that PME is not 'recommended' unless a metal grid is installed.
Now, I have discussed the word recommended with Napit and also the IET and they say it basically means it is up to the installer. It is not mandatory. However, I would have to justify why I have chosen not to use the recommendation.
2 goats, a few sacks of feed and a few plants in a massive (metal) barn (approx 75m x 25m).
What is the actual risk of sticking with the PME? Is it the potential between true earth and the PME earth. The barn will be bonded so it will be at PME earth. The ground will be at actual earth, so is the problem if the goat brushes against the metal barn whilst standing on the ground and there is a potential difference. Or, is it more to do with fault conditions?
Is this an obvious case of needing a TT, or perhaps not so obvious?
I know I have discussed this before, but now it is becoming a reality I thought I would discuss it again/further.