Discuss PME supplies to emote buildings in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Midwest

-
Esteemed
Arms
Reaction score
10,616
I've previously posted about doing a CU replacement for my assessment. I will also have to re-supply a small garage CU (20a radial + 6a lighting), which has been answer for me, thank you.

The property has a TN-C-S supply, which will be fed with new 25mm tails, 16mm EC. The garage is link detached, i.e. not separate from the house, but not integral. Do I need to consider the regs for separate buildings sharing the same supply (think it's 542.1.3.3)?

I intend to use a swa from the new house metalclad CU to garage metalclad CU. I have been reading about having same size EC for both, which seems rediculous in this case, I wouldn't have consider this in the past, but I think I have read too many books. Am I confusing the matter with larger commercial premises etc?

The garage des not have separate water/gas supplies or extraneous metal.
 
Last edited:
if the garage has extraneous metalwork, this will need bonding back to the house MET with 10mm. as it's PME.
 
If I understand you correctly, you are asking about the earthing conductor size. If you have no ECP's in the garage then you don't need to bond back to the MET. I have done several of these jobs recently and use 3 core SWA and earth the armour too. I check the Zdb at the garage, and using the adiabatic, check my CPC sizes will carry any fault current. I generally use 2.5mm 3 core SWA and you will probably find this is fine for your job too.
 
I've just reread from my copy of 'Practical guide to the 17th Ed' (by CK), which talks of more than one building sharing a supply, but having separate earth arrangements, which I'm not doing in this case, i.e. my garage EC will terminate in the main earthing terminal of the house CU. Am I right?
 

Reply to PME supplies to emote buildings in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
611
Afternoon All, Just pricing up a job and thought I'd pick your brains. Quick run-down, Block of Flats with an underground car park. In the...
Replies
27
Views
2K
Morning guys! Went to look at a consumer unit change today with a PME supply. Now, right next to this was an old BS3036 60A fused mem cutout...
Replies
2
Views
698
Hi guys, Can I ask you a DIY question? I'm refurbing a detached garage and adding a garden building. Garage currently has a submain supplied by...
Replies
1
Views
816
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
864

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock