Discuss Poor installation practice/design in the UK Electrical Forum area at ElectriciansForums.net

Ian1981

-
Mentor
Esteemed
Arms
Reaction score
3,818
currently working through a EICR on a empty care home soon to be refurbished and new clients to move in.
Distribution circuit from DB 1 feeding DB3( supplying sockets/ lighting etc) fed from a C type bs en 60898 mcb 63 amp.
Max zs 0.34(100% value)
Measured zs 0.34 ( over the 80% correction factor at site measured temperature)
DB 6 fed ( supplying sockets and lighting)from DB 3 on a 40 amp type C bs en 60898.
So a sub main feeding a DB feeding another submain for another DB all 3 phase.
A discrimination/ design nightmare all carried out in 2006, no EIC , electrical/mechanical or design drawings.
And they say domestic is bad!!
No questions to ask the forum, just a rant really.
 
It’s awful.
I’ve got ring final circuits with readings of 1.86 ohms for the line and neutral conductors because they are such large cable runs and the number of points on some of the rings reach upto 56 points!
Same with the lights, some have around 40 points where around 7 bedrooms are fed from a single circuit.
 
Get into some old industrial plants and have a look in some old control panels. No drawings, all singles, all same colour. Just a manager barking to get the thing working :)

:grinning:
Its what makes it interesting, be rubbish if everything was labelled and easy ..
 
I love doing that! Perhaps without the manager bit. Last one was good fun, all red wires no wire markers, no labels on any component or the I/O terminals.
 
Yes I see so many bad designed installations as you describe I feel your pain. I think people just think if sockets you use 2.5mm with and a 32 amp mcb or rdbo with no thought for volt drop max zs ect, and I lost count of the amount of circuits I find that have excessive earth loop impedance.:mad:
 
currently working through a EICR on a empty care home soon to be refurbished and new clients to move in.
Distribution circuit from DB 1 feeding DB3( supplying sockets/ lighting etc) fed from a C type bs en 60898 mcb 63 amp.
Max zs 0.34(100% value)
Measured zs 0.34 ( over the 80% correction factor at site measured temperature)
DB 6 fed ( supplying sockets and lighting)from DB 3 on a 40 amp type C bs en 60898.
So a sub main feeding a DB feeding another submain for another DB all 3 phase.
A discrimination/ design nightmare all carried out in 2006, no EIC , electrical/mechanical or design drawings.
And they say domestic is bad!!
No questions to ask the forum, just a rant really.
Understand your frustration fella, I have seen similar, it happens everywhere, DBs being fed off others is a very regular thing to see, it is almost the norm,
 

Reply to Poor installation practice/design in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Was having a poke around the old man's house today. Anyway. DB is under stairs (18th ed following a recent extension. Not done by me but it's...
Replies
7
Views
722
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K
Hi I'm currently doing C&G 2365 Level 3 I'm working through the 305 design assignment (Swimming pool, hotel etc.) Other then this assignment I...
Replies
4
Views
4K
The garage is 17 mtrs x 15 mtrs in the UKh The house has a 100 amp supply to the house consumer unit. The garage consumer unit is fed from a...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock