Discuss Possible problem with supply earth connection on TN-S system in the DIY Electrical Advice area at ElectriciansForums.net

Jim_e_Jib

-
Esteemed
Arms
Reaction score
519
Long time reader, first time poster.

We moved house about a year ago and had an EICR carried out before purchasing. Everything checked out fine but with a some C3 recommendations for improvement.

The power supply to the house comes up through the floor in the cupboard under the stairs. Recently I was fitting some lino in the cupboard and noticed something oil like running down the lead sheath of the supply cable. On closer inspection, the oil seemed to be running down under the soldered joint for the earth connection and onto some black cloth tape below. I gave the earth wire a gentle wiggle and whole joint rotated on the lead sheath.

It appears it is still making enough of a connection to give a good earth and pass the testing done for the EICR but it doesn't seem right. Is this something normally seen and if not, is it best to contact Western Power?


Any advice gratefully received!


IMG_20170917_171211.jpg IMG_20170917_171454.jpg
 
And..errr I wouldn't wiggle anything while you are waiting for them keep well away, that oil may be tar that is sweating out from heat on the supply cable.
 
I spoke to someone on their instant chat, they could send someone out within fours hours tonight but suggested I might like to contact them again tomorrow so they could arrange a visit at a more sensible time.

Out of interest, was the tar used in the construction of the cable or perhaps used as a sealant?
 
Last edited:
Long time reader, first time poster.

We moved house about a year ago and had an EICR carried out before purchasing. Everything checked out fine but with a some C3 recommendations for improvement.

The power supply to the house comes up through the floor in the cupboard under the stairs. Recently I was fitting some lino in the cupboard and noticed something oil like running down the lead sheath of the supply cable. On closer inspection, the oil seemed to be running down under the soldered joint for the earth connection and onto some black cloth tape below. I gave the earth wire a gentle wiggle and whole joint rotated on the lead sheath.

It appears it is still making enough of a connection to give a good earth and pass the testing done for the EICR but it doesn't seem right. Is this something normally seen and if not, is it best to contact Western Power?


Any advice gratefully received!


View attachment 39207 View attachment 39208
As Tel said contact the DNO and get that mess looked at, the bloke that did the EICR? did he not mention this to you on the certificate?
 
Hi Pete999, thanks for the advice. It wasn't mentioned on the EICR but that was done about a year ago, before we moved in, so I couldn't be sure what condition it was in then.
 
Hi Pete999, thanks for the advice. It wasn't mentioned on the EICR but that was done about a year ago, before we moved in, so I couldn't be sure what condition it was in then.
I see, but even so that earth connection must have been like that during the EICR and should have been sorted at that time. Hope you get it sorted soonest Jim.
 
time to get the blowlamp out. :eek::eek::eek:
 
I've got an old Primus paraffin blowlamp - time to dust it off, it should generate more than enough heat..... If only the matches weren't in a drawer with a childproof lock on...
 
If I understand this correctly, and looking at your picture of the earth...There appears to be heat damage to 1: the earth connection and 2: the supply cable insulation. When that "tar" starts to run it indicates heat in the supply cable. Which may in turn start to melt the solder on the earth connection to the sheath of the TN-S supply cable. If that really is the case (worst scenario!) hard to tell from here, then I would not delay getting the DNO in.
 
Thanks Vortigern. I've arranged to leave work early today and will call the DNO when I get home. They said they couldn't make an advance booking for this type of job and to call when someone would be in the house for the four hour window.

I'll let you know how it goes!
 
I used to get called to a lot of these when working for dno. Usually nothing to worry about. It is bitumen which used to bu used to fill the termination chamber on the old cut-outs. When the cut out was changed most of the bitumen is removed, but it can start to run out of the cable, more messy than dangerous. Dno will check and clean up, but not much else can be donee. They will also re-terminate earth cable.
 
Top marks to Western Power - two engineers were here a couple of hours after I rang them this afternoon. The lead has been cleaned up, a new earth connection has been made and some sealant used to stop any more tar weeping out.IMG_20171109_191907.jpg
 
that connector should have been fixed to the wall or the weetabix board and a 16mm gn/y conductor to replace the bare conductor to the CU/MET.
 
Hi telectrix, thanks for this - it seems Western Power have just lost a few marks...

Is it something I should ask them to come back to do or is it more of a good practice thing?
 
Was the original Earth soldered to the sheath of the cable, or to a constant tension spring clamp?
 

Reply to Possible problem with supply earth connection on TN-S system in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Evening Chaps As can be seen in the attached photo , the incoming supply cable has a Earth soldered to the outer sheath of the cable suggesting...
Replies
10
Views
1K
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
627
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
774
Trying to understand why car chargers attract this earthing ballache. from what I learnt it's all about the rare times a Neutral / PEN conductor...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock