Discuss Power & Cat 5 in conduit in the FreeSat, Sky, VirginMedia Forum area at ElectriciansForums.net

O

Octopus

Hi

Not sure if this is the correct forum, but can anyone help me with the following connundrum.

Need to be able to run a 230v spur and some cat 5 in surface trunking. Now clearly they can't go in the same run but are there any "nice" looking ones around with the ability to carry the 2 cables in seperate compartments.

Thanks in advance.
 
I don't have my regs to hand
however

Cat5, audio , coax comes into the range of extra low voltage which is below 100v
mains wiring whether it is single or 3 phase is classed as low voltage (upto 600v)
above that is high voltage

the different voltages shouldn't be mixed

running the mains so close to the Cat5e cable could induce a voltage and cause cross talk
 
I don't have my regs to hand
however

Cat5, audio , coax comes into the range of extra low voltage which is below 100v
mains wiring whether it is single or 3 phase is classed as low voltage (upto 600v)
above that is high voltage

the different voltages shouldn't be mixed

running the mains so close to the Cat5e cable could induce a voltage and cause cross talk
I believe, that that is why the OP wants two compartment trunking.
 
iv never had problems with data and power together -as long as its only a short run together than you will be fine - its the long runs together, say on cable tray that causes the cross talk.
 
I don't have my regs to hand
however

Cat5, audio , coax comes into the range of extra low voltage which is below 100v
mains wiring whether it is single or 3 phase is classed as low voltage (upto 600v)
above that is high voltage

the different voltages shouldn't be mixed

running the mains so close to the Cat5e cable could induce a voltage and cause cross talk

Data and power cables can be run together if the insulation of the band 1 cable (ELV) has insulation rated to the highest voltage present.
 

Reply to Power & Cat 5 in conduit in the FreeSat, Sky, VirginMedia Forum area at ElectriciansForums.net

Similar Threads

Hello, this is my first post here. I have a little experience with most types of household wiring through a decade of DIY remodeling, and...
Replies
0
Views
784
It's not that often I stare stupidly at something for 5 minutes and can't work out where to start, but.... The horizontal and lower vertical...
Replies
9
Views
2K
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
My Current Setup (see image BEFORE.jpg): The wiring for my existing detached garage is shown (see image BEFORE.jpg). The house consumer unit...
Replies
3
Views
3K
Hello all, Just had an electrician wire in a radial circuit in my house to my loft as I use the space for my home theatre equipment & wanted a...
Replies
30
Views
10K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock