Discuss Upgrading my garage electrics for more light and extra sockets in the DIY Electrical Advice area at ElectriciansForums.net

Reaction score
0
My Current Setup (see image BEFORE.jpg):
The wiring for my existing detached garage is shown (see image BEFORE.jpg). The house consumer unit provides RCD and MCB (Hager MTN116 B16 – 16A) protection and is wired to the garage via SWA. The SWA armour is earthed where it leaves the house. It enters the garage via the back of a 20AX Switch to isolate the garage and leaves out the top of this as 2.5 T&E. From here it runs to a fused spur, which provides a 3A fused 1.5 T&E cable for the single lamp and a 2.5 T&E cable for one double socket.
The light is looped in at the switch, so there is a single run of 1.5 T&E across the garage to the holder that terminates there. Similarly for the double socket there is a single run of 2.5 T&E to the socket that terminates there.

What I need:
I am based in the UK and enjoying doing woodwork and want to improve the garage to support this hobby. The single bulb does not provide anywhere near enough light and one double socket does not provide enough outlets for my needs and not enough flexibility about where I am working in the garage. I don’t have any equipment that places much load on the electrics but if I run a vacuum extractor (Henry) at the same time as my circular saw I cannot turn on the radio. Also having sockets on both sides of the garage would provide me more flexibility around where I can work on specific tasks. Additionally, as my woodworking raises lots of dust I am also keen for good IP rating and will add a glanded setup with 20mm PVC conduit where I can.

What I am planning to do (see image AFTER.jpg):
1) Existing fittings – upgrade existing fittings (see image AFTER.jpg):
move to MK Metalclad fittings (earthing the boxes and faceplates as I go) and adding 20mm conduit and glands. The current fittings have a significant amount of wood dust in them already as the plastic pattresses have no knockouts so lumps have been hand sawn out to let the cables pass, which has left large holes at the tops/bottoms of all fittings.

2) Lights – remove current light fixture and add four LED strip lights (see image AFTER.jpg): remove the existing light fixture and replace it with a junction box (say Wago XL). Then wire each of the four new LED light strips (Philips Ledinaire WT065C LED68S/840 PSU L1500) to this junction box using 1.5 flex (as the new fittings have glands/grommets for round cable only). I will use three 5-pole 221 series Wago connectors to wire all of the lives together, then all of the neutrals together and then earths together (so the live core from the switch and a live core from each of the four new fixtures will be spliced together by a 221 connector, and same for neutral and earth). I could wire/loop in and out of each of the new fixtures but I think it would be neater and may require less wire to run to a junction box that is centred between the four (as the wire from the switch across the garage already terminates here).

3) Sockets – add three new sockets (see image AFTER.jpg): My plan for the sockets is add a new double socket next to the existing one (knock out the side of the existing wall mounted pattress, pair in a short run of 2.5 T&E from it to the new socket next to it). Additionally, I would add a junction box into the existing 2.5 T&E cable that feeds these two sockets to branch off a new run of 2.5 T&E across the rafters and down the other side of the garage to create a matching pair of double sockets on the other side of the garage. All of the wiring is achieved by pairing cores (i.e., lives with lives, etc.).

QUESTIONS – I have numbered these in the hope it will make them easier to respond to:
1) Does this sound like a sensible approach for the sockets and lights?
2) The current isolator switch (where the SWA enters the garage) is 20AX rated, is it reasonable practice to replace this with a 20A rated switch instead as I am using LED and not fluorescent lights (as I found a nice 20A version at a good price)?
3) I expect that the lights will nominally consume around 1A (55W x 4/240 = 1Aish) but inrush is high (6.9A each over 50ms). I will use a standard 3A fuse on the fused spur for this lighting circuit, is this reasonable?
4) Do you have any recommendations for a junction box that may have better IP rating than the Wago XL I mentioned for the lights (ideally catering for four flex inputs and one 20mm conduit gland)?
5) Do you have a good recommendation for a 20mm gland compatible junction box for the sockets? Could I simply use three 3-pole 221 series Wago connectors in a 3 Way 20mm Tee Box for this – i.e., splice them in a conduit box?
6) A cursory run through the regs of Part P suggest that I am good to undertake this work myself (without notification or test result submission) as both are extensions to existing circuits (i.e., “additions and alterations to existing installations outside special locations”). Am I correct in this? I will also consider how this is “tested and certified in accordance with BS7671” before being connected.
 

Attachments

  • Before.jpg
    171.9 KB · Views: 23
  • After.jpg
    183.6 KB · Views: 22
The one thing you dont mention, (i think) is the size of the SWA cable.
It comes off a 16AMCB, so I assume it would be 2.5mm... However, if it was 4.00mm, you could upsize the board mcb to 32A, and put in a proper garage distribution board in place of the 20A isolating switch.
Also, if you could come out of the board on a non-rcd supply, and have RCBO's at the garage end, it would stop any nuisance trips of a faulty powertool taking out half the house.
 
Hey Littlespark, thanks for the response.

This all makes a lot of sense and you are correct. I have quickly isolated and measured the cable and it is 2.5mm core area. There is a standard run of 2.5mm T&E cable from the house CU to a junction box on the outside of the house. Here a chocblock connects it to the SWA (see image – not the neatest job).

If a garage CU/local MCB/RCD protection is needed so be it. However, this would change it from a DIY update to getting a professional in, as I would not be comfortable to undertake any work at a CU and think that this would make it notifiable in any case. Similarly, given the current carrying capacity of the 2.5mm core there seems little scope to uprate the current MCB so I would stick with the present 16A limit. Maybe in the future, if my needs change, I could get a professional to pull through some higher capacity cable, make changes at the house CU and at the garage as suggested but for now I would stay with the current setup.

I have been using the garage for around two years or so and have never had a RCD or MCB trip. Much of my work is based around manual tools so I never get close to pushing the limits on this. Also the garage is small enough that it has squashed any expectations/desires I might have to install fixed, higher load, equipment in the future – there simply is no space.
 

Attachments

  • House-Garage-JB.jpg
    332.9 KB · Views: 18
OK, so as a quick update to this. I found a junction box (Wago Abox SL-2,5/4² # 80680701, see image) that looks like a great fit for my needs. These have loads of M20 knockouts (so compatible with my conduit), IP65 rating and I found some M20 cable compression glands for my lighting flex cables.
These boxes are 24A rated so I will use these for both the socket and light junction boxes as shown on my original diagram.
 

Attachments

  • Wago_Abox.jpg
    112.5 KB · Views: 12

Reply to Upgrading my garage electrics for more light and extra sockets in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi diyer here, I'm wanting to add two extra double sockets to my garage / workshop. Currently have two double sockets wired with 4mm t+e with a...
Replies
3
Views
1K
Hi all. I'm going to replace some sockets during a routine redecoration of our lounge including replacing some singles with doubles with USB...
Replies
2
Views
693
Hi all, I'm planning to remove a stud wall seperating my dining room and kitchen. On the dining room side of the stud wall, there is a double...
Replies
1
Views
1K
Hi, just helping someone out and apologies for the long winded post. Would like install a couple of weatherproof double sockets on the patio. 1...
Replies
3
Views
743
Howdy, I'm looking for help with my plan to install an extra internal double socket and an external double waterproof socket to my garage. I...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock