Hi
I'm looking for some advice regarding power feeds to 2 garden buildings - a greenhouse and shed.
I'm aware both are covered by part p and will be getting an electrician involved but I want to check whether my overall design makes sense.

There is limited external access to the existing CU and only one spare way on the non-RCD protected side. I have buried ducting from the side of the house to the 2 buildings in preparation for pulling in SWA runs.
My design allows for 5kw per building with a local CU's (RCD, 16A and 6A MCBs) with local TT earthing.
Distances to the buildings are 20m and 50m - volts drop calcs for 5kw load gives 2.5mm2 and 6mm2 for the SWA runs respectively.
As there is only on spare main CU way I am proposing to run a 10mm (T&E) from CU (40A MCB) in the roof space (run length 12m) to a mini CU fitted with two 20A MCBs and these will feed the SWA runs to outbuildings. The SWA armour will be bonded at the house end only.
Does this sense and is the overall design OK?

Thanks
 
What is the earthing arrangement for your house?
Why TT the supply?
What did the electrician, who will be testing your circuits, say? Also what did he say about the installation method of these circuits?
 
I'm aware both are covered by part p
All electrical work is covered by Building Regulations Part P.

The legal bit of Part P (the Statutory instrument) merely says this:
4f600d0d3fb42a8fbecd8f03b02da195
 
If I am not allowed to work om ELV systems, do I need to inform building control that I have installed a door bell using a PP9 battery and a transistorised buzzer?
 

Reply to Power to 2 outbuildings from single CU way in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

So, I already have solar (an older FITS installation) and it's been particularly successful so I want to extend this. I'd like to do two things at...
Replies
1
Views
548
Hi, Need some help with an odd setup. I have a large room with many lights that i separated into 2 sets. In Box 1 there is the 14/2 power in, 2...
Replies
4
Views
1K
I'm planning a replacement for my existing domestic CU and would like to have it sanity checked before I get an electrician involved. The main...
Replies
33
Views
4K
Hi All, I have a client who is developing a plot of land for a single house. Currently, their 100 amp service cut-out is in a cubicle fed by...
Replies
7
Views
1K
I am working on putting a victron 24/3000/70 inverter/charger in my sprinter conversion van. Output of inverter is 30 amp pass thru with power...
Replies
0
Views
491

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock