    Hi
    I'm looking for some advice regarding power feeds to 2 garden buildings - a greenhouse and shed.
    I'm aware both are covered by part p and will be getting an electrician involved but I want to check whether my overall design makes sense.

    There is limited external access to the existing CU and only one spare way on the non-RCD protected side. I have buried ducting from the side of the house to the 2 buildings in preparation for pulling in SWA runs.
    My design allows for 5kw per building with a local CU's (RCD, 16A and 6A MCBs) with local TT earthing.
    Distances to the buildings are 20m and 50m - volts drop calcs for 5kw load gives 2.5mm2 and 6mm2 for the SWA runs respectively.
    As there is only on spare main CU way I am proposing to run a 10mm (T&E) from CU (40A MCB) in the roof space (run length 12m) to a mini CU fitted with two 20A MCBs and these will feed the SWA runs to outbuildings. The SWA armour will be bonded at the house end only.
    Does this sense and is the overall design OK?

    Thanks
     
  2. Spoon
    Offline

    Spoon Trusted Advisor

    Location:
    Lancashire
    What is the earthing arrangement for your house?
    Why TT the supply?
    What did the electrician, who will be testing your circuits, say? Also what did he say about the installation method of these circuits?
     
    • Optimistic Optimistic x 3
  3. suffolkspark
    Offline

    suffolkspark Electrician's Arms

    Location:
    suffolk
    CU in the roof space? um no? also did you lay any warning tape in your duct trenches?
     
  4. Leesparkykent
    Offline

    Leesparkykent You Rock Gmes Staff Member Trusted Advisor

    Location:
    Kent
    Doesn't sound good if you want to achieve discrimination.
     
  5. Taylortwocities
    Offline

    Taylortwocities Electrician's Arms

    Location:
    Oxfordshire
    All electrical work is covered by Building Regulations Part P.

    The legal bit of Part P (the Statutory instrument) merely says this:
    [​IMG]
     
  6. UKMeterman
    Offline

    UKMeterman Electrician's Arms

    If I am not allowed to work om ELV systems, do I need to inform building control that I have installed a door bell using a PP9 battery and a transistorised buzzer?
     
  7. Taylortwocities
    Offline

    Taylortwocities Electrician's Arms

    Location:
    Oxfordshire
    That information is contained in the Part P Approved Document
     
  8. davesparks
    Offline

    davesparks Trusted Advisor

    Location:
    guildford
    Why not feed both buildings with one distribution circuit?
     