Discuss Problem on job with bungalow in the UK Electrical Forum area at ElectriciansForums.net

A

axel132132

Hi

I have an issue at a bungalow im working at, there is a fault

All the sockets are on a ring, when i plug something in the living room it trips the RCD plug it into any other sockets it dosent trip the RCD

The board is MAIN SWITCH RCD

Cheers
 
Hi

I have an issue at a bungalow im working at, there is a fault

All the sockets are on a ring, when i plug something in the living room it trips the RCD plug it into any other sockets it dosent trip the RCD

The board is MAIN SWITCH RCD

Cheers

Please answer the bit in Red how have you established this ?
J
 
used to be a good code 3 on the old PIRs..... further investigation required.
 
Yeh will change socket and megger old socket at back to check if its shorted anywere thanks for help hopefully its socket and will save me some time :24:
 
is it only 1 socket that it trips on, or all the sockets in the room?
 
New posts

Reply to Problem on job with bungalow in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi. I'm in the process of getting my qualifications and am taking on some small jobs for family to try and get some experience in. Today I was...
Replies
17
Views
799
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
634
Hi, I swapped a 2 gang switched socket for a 2 gang switchless socket with usb ports downstairs. I switched off all the power to the house by...
Replies
8
Views
772
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
319
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock