Can you clever people advise as to why I might be having an issue with my ceramic kiln. I am a potter not an electrician so I will endeavour to give you what technical information I have.

11kw kiln running off a domestic board with its own 50A fuse on board in the house, 15m lenght of 10mm cable runs from house into my studio where it has its own board with a 62A breaker and 50A fuse.

The fuse in house is tripping when firing cycle reaches about 1060 degrees (kiln should reach 1250 degrees). It used to reach 1180 degrees before tripping but over a few years it has been tripping earlier and early.

The firing cycle of the kiln goes up slowly, automatically over 5 hrs automatically turning on and off until the end when its on full load. Kiln fired fine with no tripping day before yesterday (post element change) when taken fast at full load to temperature, but when I did a slower firing last night it tripped.

Kiln engineer took a reading of 45Amp and there is a drop in voltage from 240 to 232 when under load.

I have had kiln serviced and elements replaced this week and tripping still happening so pretty certain its not the kiln.

Questions: Can anyone see an issue with the electric maths? Is the cable thick enough? Can a domestic fuse be upped to next level? Can cables get tired and old?

Any advise as to what to try next would be greatly appreciated as I'm soooo frustrated with this ongoing issue.

Cheers lovelies!
 
The cable is fine in theory. It depends on how it is installed i.e. clipped direct onto a wall or in thermal insulation. Photos of the route of the cable and the "fuse"(s) you speak of will also help identify the type of MCB in use. It may be that the MCB is defective and not operating withing required parameters. The maths otherwise is fine on the design of the circuit.
 
Is your studio outside and if so what type of cable is it ( eg Armoured or PVC)? And as above , how is it run ?
 
Here are some photos of fuse and cabling. Assume its PVC and it runs underground for 2meters.

IMG_0104.JPG


IMG_0105.JPG


IMG_0106.JPG


IMG_0107.JPG
 
The cable is fine in theory. It depends on how it is installed i.e. clipped direct onto a wall or in thermal insulation. Photos of the route of the cable and the "fuse"(s) you speak of will also help identify the type of MCB in use. It may be that the MCB is defective and not operating withing required parameters. The maths otherwise is fine on the design of the circuit.

Cable is clipped onto wall, thinks its PVC. I have added photos previously.

MCB in the house is also new as I had whole new board fitted. Sorting this problem so far has cost me a fortune!!
 
Ok so thats an RCBO, (the switch in photo) so it is very likely an earth fault not a thermal aspect of the other function of that switch. So someone is going to have to test/trace where the earth fault lies.
Personally I am not sure I would have used an RCBO there with the RCD protection. Unless it is not on the circuit the RCD is governing. Sorry to get techy but someone needs to check it out for earth leakage.
 
I think Vortigern is right - needs some IR testing/leakage testing maybe.
 
Actually looking at the bend in that cable (SWA cable) outside the door it does not meet the required bend radius where it comes out of the wall and that may be your problem if I am seeing right! It may have caused the earth fault.
 
Actually looking at the bend in that cable (SWA cable) outside the door it does not meet the required bend radius where it comes out of the wall and that may be your problem if I am seeing right! It may have caused the earth fault.
Ah ok..... it also bends like that in 3 other places too...at the other end of wall and where it enters and comes out of the ground.
 
i would replace the MCB in the house with a fuse.this can be done by an electrician by removing the armoured cable from the consumer unit and feeding from a separate switch/fuse. maybe can go up to 63A, (cable calculations allowing).
 
i would replace the MCB in the house with a fuse.this can be done by an electrician by removing the armoured cable from the consumer unit and feeding from a separate switch/fuse. maybe can go up to 63A, (cable calculations allowing).

No testing or fault finding? Just straight to removing the RCBO and up-rating the ocpd?
 
sorry, dave. skimmed through the posts. never saw RCBO. of course i would test the curcuit before energising.
 
I think the 50A breaker is a bit tight for an 11kw heating load. At 232v that works out to 47.5A.
Only need a peak demand to pull the volts down a bit on the distributors transformer for the current to rise.
May also be the tolerance on the rating of the breaker is in the minus!
 

Reply to Problem with 11KW Kiln in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hoping someone maybe able to help. We have a Horstmann electronic 7 that's connected to the water heater element(everything been great for years)...
Replies
3
Views
1K
I have an electric oven - now many years old. I have replaced the main circular 2.5kW oven element (ELEHY6708) several times over the years...
Replies
9
Views
1K
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K
Hello - hope someone can advise please. I have a recently purchased second hand Myford lathe which has a 3-phase inverter (Siemens Micromaster...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock