Hello all,

I’m now overthinking the - Prospective fault current test for the 2391 practical, the exam boards will be a 3 phase and a single phase board.

Do I test the three phase board and double the highest and use that for both DB’s or do I do one for 3 phase db1 and sep one for single phase db2
 
The three phase board will be the origin, for the office just remember to record the Zdb and ipf information, top left on the schedule of test results
 
129EAEDF-A53C-47EF-8585-6963BF985CF0.jpeg
 
Test as close to the source as possible with parallel paths in place.

Test all three phases to earth then all three to neutral.

If your test meter is capable then test across all phases, L1 to L2, L2 to L3 then L2 to L3.

If you can’t test phase to phase then double the highest single phase measurement.

Do you know the difference between PSSC & PEFC?
 
Test as close to the source as possible with parallel paths in place.

Test all three phases to earth then all three to neutral.

If your test meter is capable then test across all phases, L1 to L2, L2 to L3 then L2 to L3.

If you can’t test phase to phase then double the highest single phase measurement.

Do you know the difference between PSSC & PEFC?
Yes I’m ok with that, Thank you
 
Prospective fault current at origin is the highest current, further into the installation the current will drop due to circuit resistances.
If the protective devices in the next DB are able to withstand the fault current at origin there is no need to measure again at the next DB because you already know they are OK.
 
Of course...

1) High reading on Main protective bonding conductor.

2) Low insulation resistance on the sub board / office board between neutral and earth.

3) No cpc continuity on the switch wire on one of the lights on a lighting circuit.

Also had a couple of high Zs readings due to poor connections and contact resistances.
 
Of course...

1) High reading on Main protective bonding conductor.

2) Low insulation resistance on the sub board / office board between neutral and earth.

3) No cpc continuity on the switch wire on one of the lights on a lighting circuit.

Also had a couple of high Zs readings due to poor connections and contact resistances.


Thank you,

Wish me luck my test is tomorrow
 
We had a potential of 35 fault injections and the cards were numbered and each candidate was given several random fault numbers which they injected. There is no way to know what faults you will be given. Except that there are only so many faults possible like short, no continuity, high resistance, low resistance and wrong polarity and maybe a few others all of which will be within your meters ability to spot so long as your brain is ok. Thing is to keep calm and work methodically with all fault finding.
 
What faults did you have?

A massively high continuity cpc reading on a final ring circuit,
Missing L1 connection at the socket of my 3phase motor circuit (think that’s done to make sure you test all 3 phases from the switch to the socket,
Bonding conductors not labelled.
 

Reply to - Prospective fault current test 2391 in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Does a SPD need a dedicated way? I need an extra way in this unit for a 3 phase car charger As you can see its a small unit with no extra...
Replies
45
Views
2K
Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
Replies
18
Views
2K
Hello all, I signed up here for a little help. I bought a 3 phase bandsaw and went down the rabbit hole of VFD’s etc. ‘The motor is 3 phase 400v...
Replies
9
Views
1K
Evening all, I have a little conundrum I need to get resolved. I’ve moved an EV charger from a single phase board that was on a 40a breaker and...
Replies
9
Views
610
I sorted the fault fairly quickly as it happens but only because I'd come across it once before and at the time a few people said it couldn't...
Replies
13
Views
417

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock