Discuss Pub project now under way............ in the UK Electrical Forum area at ElectriciansForums.net

Baddegg

-
Esteemed
Arms
Supporter
Patron
Reaction score
5,397
As per previous thread a wile back the pub build is now under way and upto roof level,just wanted to check my proposed electrical feed if I can please?
Earthing is TN-S not TNCS previously thought,(customer has now cleared the meter cupboard!)

Anyway loading in the pub is as follows
1 x 32a rfc 12 points
1 x 6a lighting
1 x 16a radial for ufh at 3kw (fused at sfcu)
1 x 16 a radial for water heater (no spec yet but assuming greater than 2kw)

Other loading not yet determined is a macerated toilet but hoping to spur from rfc

No extraneous parts, water and waste all in plastic
Proposed set up
Split tails into Henley and into small 2 way Cu with 100a main switch and 63a mcb, 10mm 3 core swa upto pub into sub db main switch and all circuits rcbo to relevant sizing
Have I missed anything?
As always all responses much appreciated
 
At the supply end I'd opt for a switch fuse with 60a cartridge rather than an MCB , otherwise a short circuit fault on any of the final circuits could take out the 63a MCB, the fuse gives much better discrimination. 10mm 3 core SWA should be fine depending on length of run, insulation etc, finally if the underfloor heating is running very close to 3kW I'd use a 20a DP switch rather than 13a sfcu as they don't seem to cope very well at full load current for long periods, the 16a RCBO will provide adequate protection.
 
Brilliant thanks chaps, length of run is approximately 20mtrs and the cable will be mostly in free air (under the floor cavity of house) and then under ground for about 6mtrs,
 
As the cable is partially buried you may have to go up to 16mm depending on your source fuse size. 63 amp would take you over the CCC of the cable.

With diversity you could get away with a 45 amp fuse at source.

I take it this is pub accommodation?
 
Hi strima
Thanks for that, I could get away without burying the cable but I could just as easily install 16mm as the customer isn’t to concerned on costs just safety , no not accomadation I have a customer who I’m building a 9mtr by 7mtr timber frame building in his garden. To use as a pub, pool table, darts and a bar etc..
 
As the cable is partially buried you may have to go up to 16mm depending on your source fuse size. 63 amp would take you over the CCC of the cable.

With diversity you could get away with a 45 amp fuse at source.

I take it this is pubaccommodation?

I wondered that .
You will need to find out what the cooler and cellar requirements are too if you are doing the bar .
EM lighting and alarms will need consideration too.
 
Is this an extension?sounds very small for a pub.a lot of pub chains have entertaianment sockets fed through contactor so fire alarm drops them out.apologies if have misundstood,usually work on huge buildings,but have done a few pubs in my tender years.
 
Is this an extension?sounds very small for a pub.a lot of pub chains have entertaianment sockets fed through contactor so fire alarm drops them out.apologies if have misundstood,usually work on huge buildings,but have done a few pubs in my tender years.

Yes usually councils will specify that if they have an entertainment licence.
 
No probs Simon, yeah man cave is better description I’ve just been brainwashed by the customer keep calling it that, it is a very nice man cave though, pool table, dart board, bar and poker table...
 

Reply to Pub project now under way............ in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
1K
Hi guys I have been tasked with upgrading some old rewireable fuseboards for a food warehouse that runs continually 24/7. I was asked to do an...
Replies
10
Views
2K
I'm converting my old garage into a two bedroom annex. At its nearest point it is approx 10m from main house. I plan it to be all electric, UFH...
Replies
5
Views
3K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock