Discuss Pulling 16mm SWA through 150 M of conduit? in the UK Electrical Forum area at ElectriciansForums.net

Since the cable will be down there in 100% humidity anyhow, maybe not a practical problem...

OK, since water's been mentioned, if the ducting is lying at low level or the ends are upturned and not capped, there's a fair chance of some water in the duct. This leads me to ask whether anyone's tried deliberately filing a duct with water before pulling a cable through. It would provide some lubrication (although not as good as a proper lubricant) and, maybe more importantly, it would reduce the effective weight of the cable. Any thoughts?
 
OK, since water's been mentioned, if the ducting is lying at low level or the ends are upturned and not capped, there's a fair chance of some water in the duct. This leads me to ask whether anyone's tried deliberately filing a duct with water before pulling a cable through. It would provide some lubrication (although not as good as a proper lubricant) and, maybe more importantly, it would reduce the effective weight of the cable. Any thoughts?


sounds a bit wet to me.
 
not read the whole thread , understandably at 5 pages long , but i'd want an access point left dug open every 20-30 mtrs.
trying 150mts in a single pull would be insane.
 
If a couple of labours can get enough purchase on a bit of rope to stretch that piece of armoured I will eat my hat !!! I am not talking about yanking the hell out of it , and assume a modicum of sense is being applied to the pull and the cable is correctly secured , having said that .

Unroll 150m of 16mm 3 core on a carpark, get hold of one end and pull like hell, feel the give and back lash in the cable, that's with only one person try then a couple. It's easily possible to destroy the cable in this situation.
 
Unroll 150m of 16mm 3 core on a carpark, get hold of one end and pull like hell, feel the give and back lash in the cable, that's with only one person try then a couple. It's easily possible to destroy the cable in this situation.

I must be getting cable from a different source to others then because I can honestly say that I have never seen a cable of that size " give " apart from when it is on the end of digger while being ripped out again for salvage ?
 
Don't get me wrong , I agree it is easy enough to stretch the sheath on even the largest of cables , but I just can not see how a couple of men sensibly pulling with the correct gear , can ever manage it .
 
Not wanting to disappoint anyone looking for sporting action, but I think I've made up my mind to advise a no-go without more digging. The gardener (who is the primary recipient of this cable in his shed at the end..) won't get his kettle, - or at least not very soon.

Thanks for the inputs.
 
I've just checked out how far 150m actually is...that is one frigging big garden!
If they can afford to live in a place like that, they can afford to pay for a few holes to be dug, don't make life hard for yourself for these rich basterds.

I can imagine you having friction trouble dragging it round that bend.
 
If a couple of labours can get enough purchase on a bit of rope to stretch that piece of armoured I will eat my hat !!! I am not talking about yanking the hell out of it , and assume a modicum of sense is being applied to the pull and the cable is correctly secured , having said that .


Going by that sort of statement, i dread to think of the state of some of the cables that have been pulled through small long ducts in the UK!! Going round even slow bends in a long ducted system and you'll be having to yank that cable when dead pulling, especially in a small 50 mm corrugated duct over 150 metres. ...But hey, what the hell do i know, ..Right??
 
of course the O.P. has confirmed that 16mm cable is sufficient for his lighting max volt drop over 150mtrs ..................

?

;-)
 
hahahahaha....................read the last line again:frown2:

You're laughing but i'm pretty sure some daft bugger will remember your post and fill a duct with water!! lol!!
Let's hope the water isn't on a meter, and has devised some sort of method of draining it all out. ...lol!!
 
You're laughing but i'm pretty sure some daft bugger will remember your post and fill a duct with water!! lol!!
Let's hope the water isn't on a meter, and has devised some sort of method of draining it all out. ...lol!!

To be fair I did put 2 stupid faces after the comment lol.
 
Use a cable sock, together with a cable pulling machine hired from HSS or Speedy along with the correct cord for cable pulling not polycord and it will go through slowly but surely
 
Me and my old boss tried something similar years ago. Same ducting and cable size. Duct about 80metres long with a slight dogleg at one end. We had to tie the rope to the back of my van as pulling it by hand was impossible. Managed to get it 80% of the way but the rope snapped when the SWA reached the dogleg. we dug a hole found the break and managed to finish the job but to be honest I'd never wanna do it again.

Just let the customer be aware that it might not be possible.
 
Me and my old boss tried something similar years ago. Same ducting and cable size. Duct about 80metres long with a slight dogleg at one end. We had to tie the rope to the back of my van as pulling it by hand was impossible. Managed to get it 80% of the way but the rope snapped when the SWA reached the dogleg. we dug a hole found the break and managed to finish the job but to be honest I'd never wanna do it again.

Just let the customer be aware that it might not be possible.

E54 ain't gonna be pleased with your van antics :lol: Daz
 
OP, There is some sound advice in amongst the absurdities, I would also recommend a Mandrel to test that the ducting is still "true". Running a mandrel of a slightly smaller size than interior of duct will save you a lot of heartache.

Regards

Billy
 
I had a job a few years ago to pull 70m through a 50mm underground conduit. Have to say NEVER AGAIN will I take on that kind of job as even the slightest rise or kink on the conduit can result in the cable sticking, in the end it was a case of digging several holes and and two days locating the conduit before being able to get the new cable plus being out of pocket on the job.
 
"Never again". - That's a recurring theme! I was just talking to the hire company about their winch, and they don't really know how to use it. For instance 10mm polypropylene (~ 1 tonne break, but very stretchy, maybe need to go bigger) or spend an arm and a leg on dyneema rope (winch manufacturers say use non-stretch rope).
 
"Never again". - That's a recurring theme! I was just talking to the hire company about their winch, and they don't really know how to use it. For instance 10mm polypropylene (~ 1 tonne break, but very stretchy, maybe need to go bigger) or spend an arm and a leg on dyneema rope (winch manufacturers say use non-stretch rope).

While I don't know much about pulling very long cables (and I'm going to be very wary if anyone ever asks me to now), why does it matter if the rope is stretchy? Could it be good to have some stretch in it, to reduce the mechanical shocks to the cable? Perhaps E54 or someone can advise.
 
While I don't know much about pulling very long cables (and I'm going to be very wary if anyone ever asks me to now), why does it matter if the rope is stretchy? Could it be good to have some stretch in it, to reduce the mechanical shocks to the cable? Perhaps E54 or someone can advise.

Apart from what Terminator has just stated, winches work on the basis of having an adjustable clutch which is set to slip/freewheel at a predetermined torque point, applicable to manufacturers recommendations for a given size and make-up of cable. All the cable winches i've experience of, use steel draw cables (and cable socks), though i have seen some using reinforced rope draws....

The other fact is that you shouldn't even attempt pulling cables into a continuous duct, over very long distances in one go, but then that's another matter altogether.

The point is, if carrying out a cable pull correctly, and the cable winch is continuously going into slip mode, then the pull length and or design of the cable duct is Wrong, and when those that know no better hook the cable pull wire up to a van//lorry/tractor and forcibly drag the cable come what may, through!!
 

Reply to Pulling 16mm SWA through 150 M of conduit? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, I have 50 ft of corrugated pipe buried between my house and a pool shed. I placed it where I knew future landscaping would make it very...
Replies
3
Views
488
Hi, I'm a DIY'er looking to build a 6x8 shed in my backyard in Colorado. I'm installing a gravel pad first, with 4 concrete Sonotube...
Replies
1
Views
359
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
953
I have had a kitchen extesion built on an old property (c.1810), which has an unusual consumer unit situation. Part of the property has only a...
Replies
12
Views
3K
When putting in some duct for fibre broadband we also put in a few lengths of 63/50mm twinwall duct "just in case" we needed that, as we knew of a...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock