Discuss Pulling a fuse with load on it in the UK Electrical Forum area at ElectriciansForums.net

E

ed-ectrician

One of the first things i learnt was, if you pull a dno fuse, remove the load first.

Of course i never pull fuses but that's another story...

Has anyone ever pulled one accidentally or otherwise with a load on it? What happened?!?! Bloke i work with said it's fine but he's ex military so likes to be known as a bit of a 'crazy bloke' if u know what i mean!

Not saying all ex army are like this but you do get a few like this dont you?!

Ed
 
Depends on the size of load and inductive content .... anything from a little crackle to the larger industrial racking gear that can kill you outright if PPE not used.
 
If you pull a fuse which has a load on it, there will be an arc.
The size of the arc will depend on the size of the load.
The greater the load, the greater the arc.
The main problem associated with this, is that the contacts could become welded together, or at the very least damaged.
 
I've pulled 400A rewireable fuses under load. I realy don't know what the problem is.

If you do pull them don't dither about, grab it, pull it!

If it's three phase then you have to pull two at the same time. I always went for yellow and blue, red usualy has more load due to idiot electricians loading one phase.
 
If you pull a fuse which has a load on it, there will be an arc.
The size of the arc will depend on the size of the load.
The greater the load, the greater the arc.
The main problem associated with this, is that the contacts could become welded together, or at the very least damaged.

So basically what we're saying here Mr.OP is that....tell your army friend to go to a factory, make sure everything is switched on and operational and then pull the fuse. :biggrin:
 
Domestic is relatively small even with the inductive loads found and this will limit the effect at most to a little flash and crackle ..... only minimal chance of maybe getting a burn or blinded from the vaporised metal and minute shrapnel.

Assuming no short circuit is present!!!! when refitting the DNO fuse that we all know this is just hypothetical ;)
 
Bloody nora yes under fault conditions would be nothing short of hilarious

I've see it done ed, it's not funny loading you're mate in to the ambulance.

No Way No How can you beat that fuse. Just stand back and wait for the pop.

It's more like a dull thud really with HRC fuses. Bit of a let down.
 
Now removing the explosive pellet out of an Air Bomb firework and having a spark from the fire accidently exploding it is a real bang...... and nearly lost the use of my hand and had temporery hearing loss..... when your a teen you do stupid stuff but believe it or not it never stopped me trying again .... im grown up now and spend my career trying to prevent big bangs...ironic in a sense.
 
i've see it done ed, it's not funny loading you're mate in to the ambulance.

No way no how can you beat that fuse. Just stand back and wait for the pop.

It's more like a dull thud really with hrc fuses. Bit of a let down.

and dont forget partial blindness
 
if you worried pull it fast. the chance is if your pulling it then the load wont be that great as you would have checked your not about to turn a computer or like like off...

pulled hundreds of these hypothetical fuses and never had a problem with load over it. putting back in they often crackle but turn to put them in straight so both sides hit the contacts at the same time.

- - - Updated - - -

if you worried pull it fast. the chance is if your pulling it then the load wont be that great as you would have checked your not about to turn a computer or like like off...

pulled hundreds of these hypothetical fuses and never had a problem with load over it. putting back in they often crackle but turn to put them in straight so both sides hit the contacts at the same time.
 
Another update:

Inserting the fuse under load.
Most fuse holders have a terminal shield. It has two uses. First to protect you from the live terminals, the second isn’t to well known. If you rest the fuse holder against the shield in line with the fuse contacts, you then put you’re palm against the holder and push up and in. You can’t react and pull the fuse if there’s a fault. Hold it by the handle and you reaction is pull back. Then in the words of Ellie Goldburg. “Anything can happen!”
 
Last edited by a moderator:
There was a belief at one time, that the high UV emitted by the arc, could weld contact lenses to the cornea of the eye.
Fortunately this is incorrect, although in some places the wearing of contact lenses whilst welding is still prohibited.
Not to forget the flash has vapourised hot metals and can on rare occasions get in your eye and damage your eyesight if not blind you...... imalways a fan of welders flash.... had it several times and now im more or less immune to it but its very worrying when it happens for first time :/
 
A few years back I was working at Heathrow in Terminal 1. There was a guy working on some of the large chillers and pulled out a duff cartridge fuse and replaced it with a new one, I couldn't tell you off hand what size fuse, but well over 100A if not over 200A, anyway he did this under load and it blew up. He had first degree burns over 1/3 of his body, and to top it off he was on the roof and had to crawl down the stairs, through a plant room and into a passenger lounge because he was lone working. Crazy thing is the isolator was less than 1m away.
 
Well as this is a hypothetical thread I would have to recommend that some degree of ppe be worn ie gauntlets and sheild,remember doing the 2391 had to be gloved and visored up,safety first etc,i have had to pull a fuse as no isolator of any means,i couldnt believe my eyes,callout at 7am,1/2 hr later worked back to mains room,200a cartidge in old 60s panel gone pop,no isolator on that,not even any isolator from dno onwards,called the guvnor,could not take all off load,hidden dbs etc,nightmare and not one i would like to see,dno quoted 30k to upgrade his supply which he needed,i bet its popped a few times since.
 
Not to forget the flash has vapourised hot metals and can on rare occasions get in your eye and damage your eyesight if not blind you...... imalways a fan of welders flash.... had it several times and now im more or less immune to it but its very worrying when it happens for first time :/


Cut the BS.

There is no difference between a welding flash and arc flash on the eyes.
You’ve not had a good flash if you think you can get immune to it. You would be in bed for days. The pain in you’re eyes and the blinding headaches are totally debilitating. Oh, and there’s the throwing up!
How do I know, guess.

Here's another little titbit for you, turning you’re head to the side doesn’t help. The ray’s refract/reflect through the slight bulge of the retina and make it worse!
 
I have not had a fuse blow up in my face but many years ago when using a drill that decided to go bang the arcs flew out of the casing,i couldnt see for 3 mins just complete darkness,bit of a panic as didnt know what was going on could only hear people saying you ok,optics shut down by brain to save me from further injury,was relieved when regained full sight,if thats a drill imagine what some hefty loads can do.
 
I've pulled 400A rewireable fuses under load. I realy don't know what the problem is.

If you do pull them don't dither about, grab it, pull it!

If it's three phase then you have to pull two at the same time. I always went for yellow and blue, red usualy has more load due to idiot electricians loading one phase.


That's useful to know...
 
I'll tell you what does hurt if you pull it off whilst it's fully loaded....A donkey...still,it was a petting zoo...

- - - Updated - - -

I'll tell you what does hurt if you pull it off whilst it's fully loaded....A donkey...still,it was a petting zoo
 
Never had a problem with this however I think the most I pulled is only around 40A but I will say that putting one back in under load is fun...not.
 
In the factory I work in I have to pull many circuit fuses under load up to approx 40a,
This is mainly due to the fact that none of the boards are labelled correctly so when trying to isolate a circuit its like a lucky dip!
There are approx 20 3 phase old 60s-70s MEM boards on-site and I'm slowly working my way through the labelling as well as labelling up the outlet faceplates with say "DB4S R4".
Which for the novice is - Distribution Board 4 - South Wing - Red Phase Fuse 4 (from left to right).

When pulling the fuse I always pull quick and replace quick normally with a crackle, especially the large rows of 30 flouresent tubes.
I have a knack of quickly popping them back in now, but I will always have the odd one where the pins have become slightly misshaped and does not go in a quickly as I like.

With DNO fuses in domestic settings I always ensure the load is off, if not I will not pull it.
Never been too bothered by removing seals, its the only means of isolation I have in a house so I'm obviously not going to work live on tails.
I have met many DNO chaps onsite and 99% of them know the score and if they see a new board or recent work they are not too bothered, the problem is with the newer generation of DNO engineer.
On many occasions I call the DNO after doing a CU change and ask them to come and re-seal, never had an issue with them, they are normally out to the customers within 5 days to reseal.
They normally ask what work has been done and thats it.
 
Last edited by a moderator:
This is what annoys me. You can class me as a Electrical Trainee, althogh I've got other codifications but come on, what ya thinks going to happen if you whip any sort of fuse out while its supplying a load? It's going to arc, flash, bang?
 
There's a lot of excellent information in this thread, so there's only one thing I can think of to add to it.

It's highly likely that when you nervously grip the fuse and pull, due to and excess build up of tension within the person pulling the flash and associated pop/bang will cause a little bit of poo to come out. So PPE should include some absorbant padding placed in the back of your pants to prevent fudge damage.
 
There's a lot of excellent information in this thread, so there's only one thing I can think of to add to it.

It's highly likely that when you nervously grip the fuse and pull, due to and excess build up of tension within the person pulling the flash and associated pop/bang will cause a little bit of poo to come out. So PPE should include some absorbant padding placed in the back of your pants to prevent fudge damage.

Good point I think!!, unless your tony and then you pull em out with your teeth while rolling a smoke lol
 

Reply to Pulling a fuse with load on it in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been browsing these forums for a while, always great to learn a new way to skin the same cat. Anyway, cut a long story short, was an...
Replies
11
Views
756
I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
1K
This is quite lengthy so get comfy... I had a bizarre call out relating to a job I attended about five years ago. The situation was they were...
Replies
11
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
777

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock