Simon Hall

I have a pump running for a swimming pool but after about 10 mins it trips out does any one know why this is happening it's run off a non rcd board thanks
 
Lets start again ...why is front end protection tripping?

Why isn't the overload protection sorting it out.... so assume short circuit to bypass the overload. What test have you done what results too we can all theorise but as has been mentioned lack of info'.... all due respect give us something to work on here!
 
Probably running the wrong direction, had this yesterday on a star/delta 30KW submersible pump funnily enough.

FLC went from 56 to 34 with the correct rotation.

One fot the mental notebook....always check rotation before the crane company drops it back into the lagoon.
 
Last edited:

Reply to Pump tripping out board after 10 mins in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock