My garden lighting was tripping my MCB so I checked all the junction boxes outside.

I disconnected the live, neutral and earth connections in each junction box one by working away from the house and resetting the MCB until it tripped again.

So, I’ve found it’s tripping when one box is re-connected and not tripping on the one before. Ive concluded their must be an issue with the cable which is 5 core armoured between the two boxes and is buried underground in places.

I’ve done a continuity test on each of the cables and getting a continuous beep with a reading of 0.04 or thereabouts on each cable.

I’m at a bit perplexed as to what the problem is? If the integrity of each cable appears to be good, what might be causing the cable to trip?

Is there another test on the cables I should do? Is a positive continuity test a red herring?

Any pointers would be helpful.

Thanks
 
The fault could be in the box you are reconnecting or anything connected to it.
an insulation test will normally point you in the right direction.
 

Reply to Puzzling tripping problem. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Hi, looking for some ideas on this. I went to an address on Tuesday following a storm where property has been struck by lightning. When the...
Replies
3
Views
761
Hi, I'm looking to install a new bathroom extractor fan in my bathroom as I have a windowless bathroom and the current one I have installed in...
Replies
13
Views
772
Hi all. We have a 120v 20 amp circuit to an accessory dwelling with a run of about 75' of direct bury #12. The breaker keeps tripping even when...
Replies
3
Views
339
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
681

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock