Discuss PV immersion heater proportional control in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Which btw are yours ( Ive assume solar immersion ) ??

and what others are there as personally I only know of 3 units which do this - all completely different prices and all not wanting to explain how they stop flickering - lol

I am trying hard to restrict my posts on this forum to general discussion and not use it for advertising but you have forced me into it. See our website www.intelligent-immersion.co.uk If you use burst firing you may well get flicker. If you don’t you don’t. As we don’t we don’t.
 
I have recently commissioned a 5kw wind turbine.
I requested a device to reduce export of power and they offered and fitted the immersun.
The switch has most of the bells and whistles I wanted but unfortunately my lights flickered to such an extent, when the surplus was being fed into the immersion, that I complained.
The turbine company researched the switch more carefully and decided the device was not really legal as it had no approval, so they want to remove it. This, they say, applies to all burst fire switches.
I checked out as many switches as pos and believe the Solar immersion does not use this system.
It has more or less the same options as the Immersun so I will opt for this if the turbine company agrees with me. Electronics are a bit mind blowing.

I believe it is essential to have at least 2 circuits to switch to, however what I would really like is a device which can remotely, via the ring main, switch on a selection of loads with sensing switches using various frequencies.
This would allow loads drawing from a ring main to take power when it is available or in rotation.

Regarding the immersion heater, If I cant find the remote switching I propose to EXTRACT heat from the tank when it is fully hot by running a selection of radiators through the indirect coil. This will cool the bottom area and the power will be redirected to the tank to replenish it. The pump would run when the relay diverts to the second service.
If anybody sees a flaw in this please advise.
MOST especially, if there is an electronics wizard out there will he direct me to a remote switching product.
Perhaps the switch manufacturers who read and contribute to this discussion could consider adding this to their product.


Could these not be used in conjunction with SolarImmersion or Immersun units ???

http://www.diykyoto.com/store/assets/0000/0936/Optiplug_Brochure_web.pdf

EDIT:- or these

http://www.sailwider-smartpower.com...nitoring-and-control-system-solar-version.htm
 
Last edited by a moderator:
Could these not be used in conjunction with SolarImmersion or Immersun units ???

http://www.diykyoto.com/store/assets/0000/0936/Optiplug_Brochure_web.pdf

Think you will find they only talk to a Wattson energy monitor.

Their overall concept may work for mixit but I think you need to ask about long term reliability. Units like ours may have been criticised above for being hard wired in but when you look at a Wattson type product with sensors on small jack plugs you have to ask whether it’s still going to be working in 3-5 years time. I have a cheap energy monitor with plugs like that and you have to waggle the plugs occasionally to keep it working. I also have had 3 Wattson weather stations and their average life is only 2 years before irretrievably breaking down with PCB faults. Not saying this will definitely apply to their energy products but it needs to be looked at.

A ruggedly built reliable unit is needed in this market and not one with built in obsolescence. I do happen to work as a safety and reliability engineer when not designing solar products so design safety and reliability into our product.
 
Well the first manufacturer to bring out decent "remote switched plugs" to use in conjunction with their Immersion Control kit for home automation will have access to some of my slush fund immediately.............. as I am desperate for such ability !
 
Ahem.....see here and here for a couple of downloadable brochures relating to Greenologic's Elios4You platform. It's essentially an accurate monitoring platform that will have control bolt-on features available over coming weeks, including wireless smart sockets & wireless proportional immersion control (phase angle, not burst-fire) and other features later on in the year.

If anyone wants to discuss further then feel free to contact me off-line or via PM etc,

Andy
 
Ahem.....see here and here for a couple of downloadable brochures relating to Greenologic's Elios4You platform. It's essentially an accurate monitoring platform that will have control bolt-on features available over coming weeks, including wireless smart sockets & wireless proportional immersion control (phase angle, not burst-fire) and other features later on in the year.

If anyone wants to discuss further then feel free to contact me off-line or via PM etc,

Andy

I like the look of your system but would be concerned on how quickly the initial investment could be recovered. I have just installed the SolarImmersion Mk3 (£209) and it is working really well.
Hopefully I'll be in profit after a couple of years.

It will be interesting to see how the market for these devices develops but I can't see any product with a long payback period being very successful.
 
http://solarimmersion.co.uk looks like a more professional unit and with the advanced features offered by Solarimmersion ( http://solarimmersion.co.uk ), the £29 more spend is really worth it.
Just done a trial on intelligent immersions latest unit. The unit is well built and survived my very old immersion going short circuit which is impressive. The performance is very good under all house power factor conditions which cannot be said of some rival units. I would be very nervous of solar immersions claims of only 5W export at 800W available as this cannot be achieved under normal power factor variations.
 
Thushar, EWP and echase are all promoting THEIR OWN products, along with some very shill looking support posts.. But then I am a cinic, and will probably be berated as such :)

You'll find that the leading product is promoted by installers. (see my comment in the line above :) )

If you want to know who will be around in 5 years time to support their warranties look at the companies behind each of the various products, and see how long they have been in business and check their financials - do a credit report on each of them. Also check out their current record on support and warranty support - what does each provide to an installer if one needs replacing? Then make your own decisions.

You have a few to choose from
Solar Immersion
Solic 2000
ImmerSun
Intelligent Immersion
Sola Controlla
Open Energy Monitor
Solar Cache
Solar Divert 3000

And I know I've forgotten a couple of others.

Do your own research first.
 
Last edited:
Thushar, EWP and echase are all promoting THEIR OWN products, along with some very shill looking support posts.. But then I am a cinic, and will probably be berated as such :)

You'll find that the leading product is promoted by installers. (see my comment in the line above :) )

If you want to know who will be around in 5 years time to support their warranties look at the companies behind each of the various products, and see how long they have been in business and check their financials - do a credit report on each of them. Also check out their current record on support and warranty support - what does each provide to an installer if one needs replacing? Then make your own decisions.

You have a few to choose from
Solar Immersion
Solic 2000
ImmerSun
Intelligent Immersion
Sola Controlla
Open Energy Monitor
Solar Cache
Solar Divert 3000

And I know I've forgotten a couple of others.

Do your own research first.

Thanks! Good, but could somebody (preferably impartial) please quickly summarise above mentioned proportional controllers.
Particularly info like: burst fire / phase controller; possible flickering; internet connection (via Arduino or something similar); extra benefits if any...
If you could indicate price tag would be great although I can see some prices even on last couple of pages...
I believe there are more people like me seeking this kind of info in one place.

I'm following (but not regularly) this thread for a while but to be honest I've lost a continuity. I guess as these controllers are on the UK market they should meet certain criteria for the home installation. Is that a case for all of them?

I'm about to upgrade my old combi boiler for a new condensing boiler and I'm considering to install also immersion heater as a either main source of hot water (summer) or preheat (winter) unit for the combi boiler. Obviously I would like to use surplus from my solar PV (Juraj'sPV 2.850kW | Live Output) and I'm looking for the right proportional controller for me.

Already for a year or so I'm using Sailwider (Home Energy Monitoring and Control System Solar Version with automatic operation function) controller to control 3 remote sockets for a background heating in north facing rooms to my full satisfaction.
I just hope that I'll be able to continue to use it in conjunction with proportional controller. I'm not an electrician but I do not see any reason why it should not work.
My idea is that proportional controller will feed the immersion heater up to water temperature of 60 degree and then the rest will be spread by this Sailwider controller.

thanks in advance,

Juraj
 
Last edited by a moderator:
Thanks! Good, but could somebody (preferably impartial) please quickly summarise above mentioned proportional controllers.
Particularly info like: burst fire / phase controller; possible flickering; internet connection (via Arduino or something similar); extra benefits if any...
If you could indicate price tag would be great although I can see some prices even on last couple of pages...
I believe there are more people like me seeking this kind of info in one place.

I'm following (but not regularly) this thread for a while but to be honest I've lost a continuity. I guess as these controllers are on the UK market they should meet certain criteria for the home installation. Is that a case for all of them?

I'm about to upgrade my old combi boiler for a new condensing boiler and I'm considering to install also immersion heater as a either main source of hot water (summer) or preheat (winter) unit for the combi boiler. Obviously I would like to use surplus from my solar PV (Juraj'sPV 2.850kW | Live Output) and I'm looking for the right proportional controller for me.

Already for a year or so I'm using Sailwider (Home Energy Monitoring and Control System Solar Version with automatic operation function) controller to control 3 remote sockets for a background heating in north facing rooms to my full satisfaction.
I just hope that I'll be able to continue to use it in conjunction with proportional controller. I'm not an electrician but I do not see any reason why it should not work.
My idea is that proportional controller will feed the immersion heater up to water temperature of 60 degree and then the rest will be spread by this Sailwider controller.

thanks in advance,

Juraj


Not really sure how the sailwider senses that it has available energy at its disposal, so I assume is via a CT, if so I think you may have an issue using any one of the Immersion Devices - as they may fight for use of the surplus energy and secondly do you have enough energy available for both systems |??

If you do you may find that its very seasonal when both can take advantage of surplus at somepoint during the shiny hours, but fight the rest of the time ?
 
.........snip


Already for a year or so I'm using Sailwider (Home Energy Monitoring and Control System Solar Version with automatic operation function) controller to control 3 remote sockets for a background heating in north facing rooms to my full satisfaction.
I just hope that I'll be able to continue to use it in conjunction with proportional controller. I'm not an electrician but I do not see any reason why it should not work.
My idea is that proportional controller will feed the immersion heater up to water temperature of 60 degree and then the rest will be spread by this Sailwider controller.

thanks in advance,

Juraj

Just thinking out loud now and I dont confess to know how all immersion devices work, but there are ones which have an inbuilt secondary replay such as the Solar Immersion Device which you maybe able to take advantage of to use with the Sailwider by monitoring that secondary replay????

Moves away now for the experts.........................
 
Not really sure how the sailwider senses that it has available energy at its disposal, so I assume is via a CT, if so I think you may have an issue using any one of the Immersion Devices - as they may fight for use of the surplus energy and secondly do you have enough energy available for both systems |??

If you do you may find that its very seasonal when both can take advantage of surplus at somepoint during the shiny hours, but fight the rest of the time ?


Just a quick follow on since I made this initial suggestion, I've had a brief look at your PVo and your Sailwider seems to do a fairly good job of utilising your surplus, HOWEVER its lets you down on really sunny days as if you review 25 March - you simply dont utilise all available surplus...... therefore I think you need to findout how immersion systems would interact with your existing Sailwider before moving forward with one of them - that IMO maybe the weak link for you, unless you can do as I suggested previously.
 
Just a quick follow on since I made this initial suggestion, I've had a brief look at your PVo and your Sailwider seems to do a fairly good job of utilising your surplus, HOWEVER its lets you down on really sunny days as if you review 25 March - you simply dont utilise all available surplus...... therefore I think you need to findout how immersion systems would interact with your existing Sailwider before moving forward with one of them - that IMO maybe the weak link for you, unless you can do as I suggested previously.

Hi,

exactly as you said I simply can't utilise all available surplus because Sailwider controller monitors via CT total PV generation, total consumption and in the same time it monitors what is the load on the individual remote sockets.
It switches first socket (I've got 400 W heater on it) when there is excess of 400 W, then the second based on the load on that sockets, then third and so on.
So I believe if I connect any proportional controller it will take as much as available (up to immersion rating - let say 3 kW) surplus until water is 60 degree. When immersion switches off Saiwider can use the rest of available surplus again providing there is more that 400 W surplus available.
Another option could be as you mentioned to monitor just secondary replay.

You are right living in Scotland and having 2.85 KW system is not too much :-( but in one year I've exported almost 1000 KWh and on other side I'm looking just for small 50-80 l immersion cylinder since we are just two of us.

One thing I am not sure where can I clip the proportional sensor. Is it OK on the live between meter and solarimmersion as their picture shows?
I just remember when I was first time connecting all my energy monitors (3 of them) it took me a while to understand where to clip them. I could not clip it between meter and fuse box because it could not recognise whether I am exporting or importing. So I've end up with my fuse box full of clip sensors for energy monitors and Sailwider and no space left for anything else :-(

Any chance to answer the firsts part of my previous post about summarising available proportional controllers?
 
snip....................

One thing I am not sure where can I clip the proportional sensor. Is it OK on the live between meter and solarimmersion as their picture shows?
I just remember when I was first time connecting all my energy monitors (3 of them) it took me a while to understand where to clip them. I could not clip it between meter and fuse box because it could not recognise whether I am exporting or importing. So I've end up with my fuse box full of clip sensors for energy monitors and Sailwider and no space left for anything else :-(

Any chance to answer the firsts part of my previous post about summarising available proportional controllers?

The Immersion Device CT sensor will always have to be on the tails just after the DNO electric meter and senses current in both directions, or at least I know the Solar Immersion CT does. This way it picks up all current movement and knows precisely the net surplus available.

Unfortunately I do not have enough product knowledge of each device to give you a summary of each but a few suppliers have offered that information in various posts, some havent !

All I can tell you is in a normal situation - they all work and use surplus, supplied at different purchase costs, if you want to know finer details, you need to speak to both suppliers and some of their existing customers.

hth


ps> Note for all - to a certain degree there is a benefit of these devices in conjunction with OLD DNO meters - it will in the majority of cases stop the meter going backwards in naturally the right conditions - lol
 
Unfortunately I do not have enough product knowledge of each device to give you a summary of each but a few suppliers have offered that information in various posts, some havent !

All I can tell you is in a normal situation - they all work and use surplus, supplied at different purchase costs, if you want to know finer details, you need to speak to both suppliers and some of their existing customers.

hth


ps> Note for all - to a certain degree there is a benefit of these devices in conjunction with OLD DNO meters - it will in the majority of cases stop the meter going backwards in naturally the right conditions - lol

Hi,

Is Solarimmersion phase fired controller? Somehow I can not get this info from manufacturer :-(
I can see that you are using this controller. Is it reliable or any issues?
Thanks,

Juraj
 
I'm about to upgrade my old combi boiler for a new condensing boiler and I'm considering to install also immersion heater as a either main source of hot water (summer) or preheat (winter) unit for the combi boiler.
Juraj

The unit in my house is generating too much hot water at this time of year, partly because I also had a solar thermal systems installed some years ago. What is the view on feeding combi boilers off the hot water cylinder?

We have 2 gas boilers in our house and although the main boiler goes off for 6 months in a year the combi one that feeds our granny annex has to stay on because it not possible to feed its taps from the cylinder due to a long pipe run. Problems I can see with feeding the combi are:


  1. They are mains fed. Is around 0.5bar from the cylinder enough pressure? It will drop as flow rate goes up. The radiator loop will still be at its usual 1 to 2bar.


  1. What happens if the feed water goes up to 70C and the combi is only trying to generate 50C? Hopefully the gas will go off but the water still flows through the combi.


  1. Due to long pipe runs, around 4 to 8 litres has to flow before the cylinder water reaches the combi. So for short uses, like washing up, the hot water is never going to get to the combi. As the feed pipe can not be insulated due to its inaccessibility it will often cool down again before the next use.


  1. Are they any water regs reasons to not do this?


Anyone tried this?
 
If you want to know who will be around in 5 years time to support their warranties look at the companies behind each of the various products, and see how long they have been in business.

A lot of the companies in this field are quite new and so there is indeed a risk that your support lifeline will fail if they do not last. The important thing therefore is to get a reliable product that will last you many years even if the company vanishes. E.g. does it have a fuse to protect itself against load failure as otherwise the unit could be toast with no warrantee cover if your immersion fails, as they often short circuit at end of life?

Apart from a couple of units that blew their easily replaceable fuses because of an immersion failure we have never had an in-service failure, but to be fair to Immersun we have not sold as many units as them so would expect less failures than they. Why has Navitron apparently stopped selling Immersuns if they are the leading product?

I have been in this business for 2 years and with another solar product long before that that I still support although it pays me no money. I would continue support out of interest in the technology and not because of any commercial imperative.

Or you could say that with such good paybacks you will have recovered your money in a short number of years. So if it then fails out of warrantee it’s not the end of the world because by then you can probably buy a replacement at half the price.
 
Last edited:
echase on solution for you:
Pumped mains pressure (i.e permanently circulating) hot hater is a commion feature in premises with long hot water pipe runs and is used a lot of commerical premises, ideally of course going through a thermal store, that way hot water is always hot instantaneously.You need effectively a 'ring main' of hot water pipes to do this of course.
 
echase on solution for you:
Pumped mains pressure (i.e permanently circulating) hot water is a commion feature in premises with long hot water pipe runs and is used a lot of commerical premises, ideally of course going through a thermal store, that way hot water is always hot instantaneously.You need effectively a 'ring main' of hot water pipes to do this of course.

My last house had such a pumped system but it had been disconnected, presumably because of the heat losses from constantly circulating it in uninsulated pipes mostly buried in the concrete floor. Running its standard CH type pump all the time to circulate it can’t have been very energy efficient either.

I could do it on this house for the annex only, but would need a small pump and/or a control system to keep the losses down, e.g. turn it off when no occupancy/movement detected. Or detect the pressure drop when tap turned on and then starting the pump like caravans use. If it were a CH pump on full speed it would then pump the hot water to taps pretty quickly. Are there standard ways to control this?
 
My last house had such a pumped system but it had been disconnected, presumably because of the heat losses from constantly circulating it in uninsulated pipes mostly buried in the concrete floor. Running its standard CH type pump all the time to circulate it can’t have been very energy efficient either.

I could do it on this house for the annex only, but would need a small pump and/or a control system to keep the losses down, e.g. turn it off when no occupancy/movement detected. Or detect the pressure drop when tap turned on and then starting the pump like caravans use. If it were a CH pump on full speed it would then pump the hot water to taps pretty quickly. Are there standard ways to control this?

Grundfos do a range of secondary circulation pumps starting at around £120.00. I have used a basic one in our own house in conjunction with a Horstmann Channelplus H47XL four channel timer. (CH, HW, UFH, & secondary circulation). It is timed to come on when hot water is mainly used. Every pipe is insulated to within an inch of its life. System monitoring shows we are loosing very little in terms of temperature drop on return to the tank. Absolute bliss to turn on the shower and get straight in.
 
My last house had such a pumped system but it had been disconnected, presumably because of the heat losses from constantly circulating it in uninsulated pipes mostly buried in the concrete floor. Running its standard CH type pump all the time to circulate it can’t have been very energy efficient either.

I could do it on this house for the annex only, but would need a small pump and/or a control system to keep the losses down, e.g. turn it off when no occupancy/movement detected. Or detect the pressure drop when tap turned on and then starting the pump like caravans use. If it were a CH pump on full speed it would then pump the hot water to taps pretty quickly. Are there standard ways to control this?

Not circulating it would give no benefit of a 'standard' mains pressure combi or unvented system. Yes there are standard pressure drop controllers - think power shower. As for movement sensors triggering a pump, just use a normal PIR linked up to a contactor. Simple inexpensiive Din rail mounted contactors form Chint NO or NC. However see The Solar King's post you do need to insulate well.

We picked this up on a refurb project we visitied the other day that also had pumped hot water - no insulation at all, I pointed it out to the owner who immediately got the plumber back on site :)
 
Danesol, as is often stated on these threads, announcing trade prices is not very helpful; we all need to make a living. However I can see that Immersun is being offered on-line fitted for £495 including VAT and I am sure you could get the iBoost fitted for a similar price.
 
Danesol, as is often stated on these threads, announcing trade prices is not very helpful; we all need to make a living. However I can see that Immersun is being offered on-line fitted for £495 including VAT and I am sure you could get the iBoost fitted for a similar price.


That is very true CBR600 and the way it should be especially for trade only sites, however this is an "open forum" so threads which contain both retail & trade pricing could get confusing for some.

I noticed you only made comparison to the Immersun & Solic 200 as a trade price fit which is fair enough, however when members viewing on, see this in comparison to the supply of devices like the SolarImmersion and i2 at £ 229 and £ 199 delivered respectfully which I may add are just as good if NOT better - to me that can more of a negative effect for good PV Installers & Electricians alike as it shows to propective clientèle they are either been ripped off or the units themselves are way way too dear, as any competent electrician/installer should be able to fit anyone of these devices between 30 to 60mins and at £ 75 p/hr say - that ain't much ontop of £ 229 for Solar Immersion giving a top estimated fitted price of say £ 304, a saving therefore of £ 191 on the likes of the Immersun, Solic200 and the one you are mentioning - iBoost
 
I am not quite sure how I am being pulled into a discussion about pricing, my original question was about iBoost and if anyone had any experience with it so perhaps we can discuss that. If you have I would be very interested to to hear! Alternatively, if you have experience of fitting another device that communicates wirelessly I would be very interested to hear about that too as this is my primary interest in this device.
 
I am not quite sure how I am being pulled into a discussion about pricing, my original question was about iBoost and if anyone had any experience with it so perhaps we can discuss that. If you have I would be very interested to to hear! Alternatively, if you have experience of fitting another device that communicates wirelessly I would be very interested to hear about that too as this is my primary interest in this device.


The very reason you are been pulled into a discussion on pricing is that is so important to most, there's no point IMO paying more if unit.A can do exactly what unit.B can do for £200 less.............. otherwise you just hope the more expensive item comes with a 25yr warranty :)

IMO, there is very little difference from the user prospective, in how all these different makes & models undertake their primary task - divert excess electric proportionally to your existing Immersion Heater element. However you may want to pay a little more for say reporting and having a secondary relay as standard or linking into to other products such as the Elios Monitoring system.........

I did want a wifi device initially, but I eventually decided against it due to battery longevity and associated issues and just did the donkey work necessary to pull a cat5 cable through to extend the CT sensor.

However, after all that the iBoost is a nice looking device if you are going to have it on show, unlike me with mine in the airing cupboard .................
 
Or these 3 Immersuns powering 4 x 4.5kW = 18kW of 3 phase immersion mounted above a 2500 ltr thermal store in the basement of biomass heated and PV powered building :)
1-IMG_1880.JPG
 
So assuming it’s the same Immersun burst fire unit it’s just as non complaint with mandatory electrical specifications in most installations due to its light flicker inducing tendencies.

I can’t understand why people still install these burst fire devices when the problems are well know. Immersuns (and any rebranded ones based on it) are the only burst fire commercial devices as far as I am aware. Others use alternative techniques like phase control to avoid light flicker.
 
Can anyone out there please respond to CBR600's original question about the solar iBoost? I am also keen to get some information from the experts on this product. :20:
 
Can anyone out there please respond to CBR600's original question about the solar iBoost? I am also keen to get some information from the experts on this product. :20:
what specifically would you like to know?

The unit works, seems reasonably reliable, is simple to fit, other than the odd time where the radio range isn't sufficient, but that';s only happened once to us and was simply fixed by moving the transmitter inside from the external meter cupboard we'd originally fitted it in.

they probably still aren't flicker regs compliant in all circumstances, though I think they're significantly better on this score than the original Immersun. We're in the process of switching across to the Elios4U units because they're fully complaint.

I've also just ended up with 2 oscilloscopes, so might try to have a play and test all 3 units next to each other and see what they actually do to the waveforms in different situations, that's if I ever get the time.
 
We have installed few and like the fact they are easy to install and have wireless clamps.

I am ordering my first power reducer with elios4you tomorrow for a customer, haven't had any experience with the Elios yet and like the fact the power reducer is the only EMC compliant product so i look forward to checking the products out.
 

Reply to PV immersion heater proportional control in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

I need a 3 phase immersion heater with a DN32/42 mm thread for a commercial pasteuriser. The only ones that I've found so far are not inexpensive...
Replies
0
Views
612
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
845
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
220
Hi, Have normal fused immersion heater switch. I would like to add a smart wifi switch to it so when my Solar is producing over 3k spare, going...
Replies
2
Views
2K
HI Folks. This is my first post so apologies if it's in the wrong location. I recently installed a 3kw Solar system with an iboost diverter...
Replies
15
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock