Discuss Question Regarding Adding Wiring To Lighting Circuit / Going Down A Cable Size in the Lighting Forum area at ElectriciansForums.net

ZEDEZ

-
Reaction score
51
I've got a lighting circuit wired in 1.5mm T&E on a 6 amp MCB. There are some lights that I'd like to add on to this circuit, controlled by an existing switch. Due to the position of these lights, the most aesthetically pleasing way to install these lights would be to run cable to the new lights from the furthest existing light, using 0.75mm flex, surface clipped direct.

If I remember correctly, 0.75mm flex is rated for 6 amps.

Provided the additional wiring doesn't push the Zs too high, is there any reason why this shouldn't be done?
 
why not use 1.5mm flex. it's only a bit bigger, diameter wise.?
 
why not use 1.5mm flex. it's only a bit bigger, diameter wise.?

I could, but it wouldn't look quite as nice. 0.75mm is just the ticket in this case.

Still, even if I was to use 1.5mm flex, I'd still like to know whether using the 0.75mm would be acceptable.

I can't see why it wouldn't be, but I have a niggling feeling there's something I'm not taking into consideration.
 
ah got you...I read it as any other application i.e other than lighting, power, etc lol.

Ah yeah I see what you mean. I am sure it refers to any other application than a specific appliance.

That said I would not use it myself in the situation in question here, only if fused down. I know it may be allowed by the minimum sizes and CCC charts but it wouldn't feel right, and I'm funny like that.
 
Ah yeah I see what you mean. I am sure it refers to any other application than a specific appliance.

That said I would not use it myself in the situation in question here, only if fused down. I know it may be allowed by the minimum sizes and CCC charts but it wouldn't feel right, and I'm funny like that.
IIRC the maximum length after a reduction in CSA is 2m.
 
IIRC the maximum length after a reduction in CSA is 2m.

433.3.1
Where a reduction in CCC occurs but the most onerous CCC in any part of that circuit is protected by the OCPD then omission for overload protection at the point of reduction is allowed and not subject to any maximum length.
 
433.3.1
Where a reduction in CCC occurs but the most onerous CCC in any part of that circuit is protected by the OCPD then omission for overload protection at the point of reduction is allowed and not subject to any maximum length.

Boom, that's great Andy, thanks!
 
Interesting! Can you see any issues with what I was suggesting Andy?

Not on the face of it. I personally like to keep the cable size constant throughout a circuit if possible and Tel's suggestion of 1.5mm flex would probably be my way forward.
As long as the EFLI, VD, and circuit loading is kept an eye on I can't really see any problems though.
 
To be honest , I have never used flex for fixed wiring. I was thinking if he must , at least use 1mm as a minimum.
I would not turn a job out like that.
 

Reply to Question Regarding Adding Wiring To Lighting Circuit / Going Down A Cable Size in the Lighting Forum area at ElectriciansForums.net

Similar Threads

Hi all, First post here, hope I'm compliant with the rules! I did do a quick search before asking this, but I couldn't quite come up with the...
Replies
3
Views
3K
Hi all, Got an antique light fitting that for some reason she wants putting up (can't say I love it haha) however it didn't come with any...
Replies
9
Views
3K
Hi all, looking for some clarification on MCB and cable sizes I need to run for a new kitchen. Cables will run through a combination of...
Replies
0
Views
3K
Hi all, I'd like to replace some MR16 halogen fittings on an exposed wooden beam to new GU10 fittings which I will be fitting led lamps into. The...
Replies
2
Views
1K
I thought that I posted this in the DIY part of the forum but I believe I did not. I am sorry about that. I put in a 10' x 20' metal shed about...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock