Discuss R1 + R2 on commercial eicr. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
26
R1+R2, quick question, if you couldn't locate the corresponding cpc could you just link the line conductor to the cpc/earth bar and test at the furthest point for R1+R2 on a radial circuit?

I know the non-corresponding cpc / neutral would be a C3 but would be nice to get R1+R2 this way instead of just an R2 using the long lead (which i tend to use anyway).

your help much appreciated.
 
R1+R2, quick question, if you couldn't locate the corresponding cpc could you just link the line conductor to the cpc/earth bar and test at the furthest point for R1+R2 on a radial circuit?

I know the non-corresponding cpc / neutral would be a C3 but would be nice to get R1+R2 this way instead of just an R2 using the long lead (which i tend to use anyway).

your help much appreciated.
you could r2 to find the right cpc
 
true, would involve a lot more dismantling work though, would probably be easier to list as a limitation and requires further investigation, R2 using long lead and C3 the board for non-corresponding cpc/neutrals.
 
true, would involve a lot more dismantling work though, would probably be easier to list as a limitation and requires further investigation, R2 using long lead and C3 the board for non-corresponding cpc/neutrals.

Limitations are something to be agreed before you start, not a means of making the job easier by avoiding doing it properly.
 
R1+R2, quick question, if you couldn't locate the corresponding cpc could you just link the line conductor to the cpc/earth bar and test at the furthest point for R1+R2 on a radial circuit?

I know the non-corresponding cpc / neutral would be a C3 but would be nice to get R1+R2 this way instead of just an R2 using the long lead (which i tend to use anyway).

your help much appreciated.

That's what the OSG shows. Unfortunately what they forget to tell you is that any supplementary bonding, metal containment on the circuit under test, or other fortuitous connections to earth may skew your results.

As this is an EICR, all you need to establish is that there is a connection to the MET and that the loop impedance is satisfactory for the correct operation of the protective device.
 
Agree with above. On an EICR it would not necessarily be worthwhile carrying out an R1+R2 test. That test is intended for initial verification BEFORE energising a circuit. On an EICR the circuit has already been energised,if Zs test results are as expected then thats good enough. I would only carry out R1+R2 tests on circuits where Zs readings were not what I would expect.
 
Thanks all, I know that there is risk attached but how many of you do the live Zs test at the furthest point for all circuits? I know it's what's agreed with the client etc etc but i try to get as close to 100% Zs as is humanly possible (or reasonably practicable as they say!). I then go for L-PE and then L-N insulation resistance followed by R2 long lead or link L-PE at DB and test at furthest point for R1+R2. I mainly go for this as most of the time previous records are flaky at best.
 
on a side not, working in an old single phase wylex metalclad board today, neutrals and earths all over the shop along with old cables cut off and left and others just left with tape around......... decided to have a word with the funeral home manager and got permission to turn off the board to make good........ all old crap now removed and neutrals and earths in the correct numbered terminals. Felt good after that :) can carry on testing it tomorrow now :)
 
i hadn't started testing at that point, i was doing the inspection precedes testing bit, opened the board to see a rats nest, sought permission, isolated board, made good all issues and testing will now commence tomorrow.......
 
Thanks all, I know that there is risk attached but how many of you do the live Zs test at the furthest point for all circuits? I know it's what's agreed with the client etc etc but i try to get as close to 100% Zs as is humanly possible (or reasonably practicable as they say!). I then go for L-PE and then L-N insulation resistance followed by R2 long lead or link L-PE at DB and test at furthest point for R1+R2. I mainly go for this as most of the time previous records are flaky at best.

As you're doing it anyway, I would do the R2, or R1+R2 first - if the cpc is not properly connected at the db (or somewhere else) your loop test will put 230V on any connected exposed- or extraneous-conductive-parts. May be OK if there is no one else about, but you need to consider the risk.
 
Thanks all, I know that there is risk attached but how many of you do the live Zs test at the furthest point for all circuits? I know it's what's agreed with the client etc etc but i try to get as close to 100% Zs as is humanly possible (or reasonably practicable as they say!). I then go for L-PE and then L-N insulation resistance followed by R2 long lead or link L-PE at DB and test at furthest point for R1+R2. I mainly go for this as most of the time previous records are flaky at best.
Your testing is completely in the wrong order which could be dangerous and the results could under certain conditions be meaningless!
 
Last edited:
Indeed it does. However, following the "correct order" saves you having to backtrack when you find, for example, that you've performed the IR test lives to earth, but your subsequent R2 wander lead test proves that you don't in fact have a connection to earth, rendering the IR results meaningless.
 
Last edited:
Indeed it does. However, following the "correct order" saves you having to backtrack when you find, for example, that you've performed the IR test lives to earth, but your subsequent R2 wander lead test proves that you don't in fact have a connection to earth, rendering the IR results meaningless.

point taken, as an example, testing at a funeral care home this week, lots of metal decorative fittings on the wall, first job of the day while quiet in the place got my R2 long lead out and had a good walk around testing the metalwork of the fittings, couple had no earth traced to bad fly lead on fitting, global IR on the board later and finally Zs all points..... every days a new routine.
 

Reply to R1 + R2 on commercial eicr. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi guys Completed an EICR yesterday. One of the Sockets Radials had no CPC so R1+R2 plus Zs could not be not be completed. Does anyone know the...
Replies
14
Views
610
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
854
Looking at the EICR form. GENERIC SCHEDULE OF TEST RESULTS Looking for clarification on R1,R2,Rn versus r1,r2,rn continuity values. I have...
Replies
9
Views
7K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
870
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock