sxsparky

My meter seems fine but when measuring r1+r2 the reading really seem to jump about from 0.31 up to 0.71 is this normal on sockets

Why do the readings jump about on a ring figure 8. Test

R1 end to end was 0.61 rn was same and r2 was about 1.66 x r1
 
please edit post so we know when you mean r1,r2 and R1,R2. so confusing, mate.

and the reason the readings vary is usually crap sockets.
 
socket connections, socket quality, leads. meter batteries going low.
 
Tested leads all seem fine, new batterys fitted, mk sockets r1, r2 rn are all fine just R1+R2 could the quality of the terminal block used to join at the board do this. As they are not the normal ones i use. Picked them up in trade point has hard white plastic coating and dont look brass or copper.
 
please edit post so we know when you mean r1,r2 and R1,R2. so confusing, mate.

and the reason the readings vary is usually crap sockets.

Sorry mate using my phone and.keyboard is rubbish lol and not sure how to edit this post but i mean big R1+R2 hope you can forgive me :)
 
that's what happens when you use something that'e designed for making phone calls as a typewriter. it's bad enough with these big keys.LOL.
 
drop socket and test straight from terminals, socket adaptors don't make good contact in worn sockets. from figures it looks like old 2.5t+e with 1mm cpc. probably some dodgy connections in there somewhere also.
 
Last edited by a moderator:

Reply to r1+r2 on ring figure 8 readings in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi All, Had a weird one this morning during an EICR. Testing a ring final circuit in a 2 bed flat… kitchen was on a separate ring. With only the...
Replies
7
Views
1K
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
875
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
After fixing a few CPC related issues on a ring final I got the following results L-L = 0.47 N-N = 0.47 CPC-CPC = 0.69 R1+R2 Tested at 0.31...
Replies
3
Views
1K
Hi so i am doing a test on sockets on a ring Final circuit for family member. Got my end to ends r1 0.62, rn 0.64, r2 0.97, identified opposite...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock