Search the forum,

Discuss R2 test on a ring main where the conduit is the earth in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

K

Kev2632

What readings would expect for the wandering lead method whilst testing from the consumer unit to the sockets, would you expect in the region of less than 0.10 ohm?
 
yea its a ring final but the conduit is the CPC and once ive deducted the resistance of the "wandering lead" im getting less than 0.10 ohm for the resistance of the conduit, does that sound right?
 
yea its a ring final but the conduit is the CPC and once ive deducted the resistance of the "wandering lead" im getting less than 0.10 ohm for the resistance of the conduit, does that sound right?
so from yesterday, we can deduce that the fault is on the live or R1 part of the circuit giving you greater than 200 ohms overall.
 
yea when i moved onto the Ringmain im getting less than 0.10ohm for the R2 reading on the ringmain circuit does that seem to be right ?yea
 
you didn't mention yesterday it was a ring final. Have you taken all the socket fronts off?

im on a different circuit than yesterday and all im wanting to do is get my R2 reading for the ringmain and im getting less than 0.10ohm for the ringmain does that sound right? its a 1 storey 1 bedroom house really small.
 
i'l chance it and say yeah, sounds about right. You're spending some time testing this house!

yea thats what i was thinking ye, you always expect really low readings like that yea, with a small house and when testing for the R2 reading yea??? nahh ive been busy with other jobs and that this last two days, only got a wee while here and there at it like.
 
yea, well let me take a pull of this here spliff while i think, nahh, bad weed, poor joint somewhere.
 
Low readings on a conduit system R2 reading is what you want and the reading you got was fine. remember its a big lump of metal and a high reading would indicate bad joints!! and a bad joint really aint what you want.. Telextrix pass round what ever that is :)
 
So it's still eligible to do the r1+r2 test on the ring main where the conduit is the CPC yea? Just link at board and test at each socket yea?
 
A wander lead is the correct method of testing conduit containment systems, though far better using a high current ductor tester!! All conduit system fed accessories should have a flying lead from box to face plate. Don't know why anyone would think you can't carry out ELI tests on conduit systems without a separate CPC?? You just don't, or shouldn't need them!!
 
it's a bit like earth bond testing when doing PAT. high current, but a more accurate resistance measurement. the high current will show up any corroded joints in the conduit.
 
Ive never come across or wired a conduit system using it as the earth. Always been in the spec that separate cpc needed. What is a high current doctor thingy then 54?

Shouldn't really be calling it a Ductor tester really, as Tony Say's a true ductor tester is generally a high current milli/micro ohm tester!! It's basically a high current ohm meter that tests the bonding/continuity of conduit/trunking containment systems on a wander lead basis. Most used to know these bit's of kit as the ''Clare Tester'' The early ones used to come in an integral wooden case...

Never seen a professionally produced electrical specification that calls for a separate CPC to be pulled into a metallic containment system, as it's a costly and totally pointless exercise!!!
 
well so far I have done two schools, a college, a hospital and a fire station in steel trunking and conduit and have pulled in same size pvc single cpc in every one. Labour only so I'm not worried about the cost lol.
 
I'll just point out again, a totally pointless and costly exercise!!

Thankfully, i've never seen such a specification in all the years i've been in the industry!!
 
Most used to know these bit's of kit as the ''Clare Tester'' The early ones used to come in an integral wooden case...

Woe betide you if you forgot to put it on charge at the end of the day!
God help you if Jim the tester’s mate found you’d got dirt on the polished wooden case! The ones we had wouldn’t have looked out of place on mother’s sideboard.
 
Woe betide you if you forgot to put it on charge at the end of the day!
God help you if Jim the tester’s mate found you’d got dirt on the polished wooden case! The ones we had wouldn’t have looked out of place on mother’s sideboard.

Many of these conduit testers were mains powered units, in fact i can't say that i've used a battery unit myself... lol!! But your right about those older wooden boxed units, works of art they were!!...lol!!
 

Reply to R2 test on a ring main where the conduit is the earth in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Hey there, Sorry I’ve just joined up. I’m a qualified electrician/Electrical engineer. Recently sat my 2391-52. My question is I had a fault...
Replies
4
Views
1K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top