Tradewind25

I currently have an integral garage fed by a radial circuit protected by a 32A MCB and wired with 4mm T&E cable. This feeds just two power points in the garage (and nothing else).
i wish to redesign this circuit to provide several more power points and would like to check whether my proposed design is within regulations. What I foresee is a number of junction boxes wired in series in 4mm cable. From each box would be a single power point wired in 2.5mm T&E cable. In effect, all outlets on the circuit would be spurs.

i would be grateful of your professional comments on this design. (I am aware of tge 33m total cable length restriction.)

Regards
Geoff
 
Hi Tradewind25 welcome to the forum ... you are down as retired but don't specify, so with can put your query in the correct section can you tell us if you have any electrical background thanks.
 
OP - Be very careful, your design describes dropping cable size from the junction boxes which is a no go.

Please make sure you complete your circuit design calculations before undertaking any work - what is your proposed maximum demand? Also, what is the supply type?
 
just carry on with 4mm, socket to socket. any branches in 4mm. and they're not spurs unless off a ring, on a radial they're branches. just be careful that your calculated load is < 32A. if you want lights, fit a FCU fused @ 5A.
 
The total load at any one time is unlikely to exceed 13A. I simply wish to have a greater choice of sockets to use around the garage wall. The space in question is approx 6x7 metres. There will be no lighting off this circuit.

I read in several threads on the topic of radial circuits (not necessarily on this forum) that, although a 32A protected circuit has to be wired in 4mm cable, "spurs" may be taken from a socket on the circuit and wired in 2.5mm cable. As I see it, under my proposed design I am simply replacing the radial sockets with junction boxes.

The reason I do not wish to create a simple radial circuit is that I do not want horizontal runs of cable at socket height; I prefer the main cable run to be at ceiling height. To then drop two cables to each socket would inevitably mean my contravening the 33m limit.
 
Go with Tel's post, keep with the 4mm, if you insist on spuring with 2.5 with your drops, change the mcb to 20amp.
 
OK guys, I give in - I'll use 4mm cable throughout.
Just to be clear, I am correct in thinking that the rest of mynproposed design is OK? I.e. All sockets are wired as spurs from junction boxes.
 
Why would you want to do it this way rather than cable in and back out of each socket? The more joints the more problems and the less reliable.
 
I may be misunderstanding, but they wouldn't be Spurs as its a radial circuit. the junction boxes would be joints in the circuit.
 
DIYer's luv a JB or three!
FYI: This DIYer has a first class Electrical Engineering degree. However that was many years ago and I am far from up to speed with currect Regs. I had hoped that this forum would provide reliable advice, rather than facetious comments.
 
FYI: This DIYer has a first class Electrical Engineering degree. However that was many years ago and I am far from up to speed with currect Regs. I had hoped that this forum would provide reliable advice, rather than facetious comments.

Forget the degree, just use a little common sense!
Every joint is a potential point of failure, common sense says you don't add a load of unnecessary joints.
If you are insistent on adding unnecessary joints then why not use 4mm for the branches?
 
If you are insistent on adding unnecessary joints then why not use 4mm for the branches?
1. I have already agreed that 4mm throughout would be better.
2. The "unnecessary" joints are due to my understanding that there is a max cable length.
 

Reply to Radial circuit and the use of spurs in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi, I`m looking for an advice. I have an electric shower that I`m not using due to boiler changed to combi and added shower over bath feed by a...
Replies
1
Views
928
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
633
Hi everyone. I should start by saying I'm not sure I'm in the right place here (this isn't a householder issue - I'm making a Ghostbusters...
Replies
20
Views
1K
Hi! I've got a couple of 32A Wago clips. Creating a spur socket from a ring circuit with these is quite easy, but I wanted to know if it's...
Replies
10
Views
1K
Client currently has a DB in his outhouse. It feeds a pool pump and an air source heat pump. It is currently being supplied using a 4mm T&E cable...
Replies
9
Views
632

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock