Discuss Radials V Ring mains in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

I also ran 6mm radials whilst working in Canada @110Volts using MK 110V socket outlets, had nil trouble with connecting them up either. Just saying.

I cannot understand how someone can be working on electrics in Canada and not know the voltage is 120v plus or minus 5%. 110v is a myth and outside the permitted tolerance.
 
I cannot understand how someone can be working on electrics in Canada and not know the voltage is 120v plus or minus 5%. 110v is a myth and outside the permitted tolerance.
Hi check regulations , can use radial 2.5 mm serves 50 square meters 20 amp cb& 4mm at 75 square meters 32 amp cb
 
If you think about it, if you take an RFC wired in 2.5 and supplied by a 32A MCB and: remove one section of cable, and split the tails across two 20 or 25A MCBs then you have :
  • Increased the total available current from 32A to 40 or 50A
  • Reduced the amount of cable used
So the two radials (assuming a new install or a rewire) will need less cable and provide a higher total load capacity than the same outlets wired as an RFC. You've also (assuming RCBOs) reduced the amount of stuff that goes off when a breaker trips.
However, you've also increased the volt drops. So if the alternative RFC was on (or near) the limits, the two radials would most likely be over the limits for volt drops.
 
Increased the total available current from 32A to 40 or 50A

However, you have also restricted where the current can be used. With a 32A circuit, regardless of whether it is radial or an RFC, you could spread 32A around half of it, or all of it, and nothing will be overloaded. With two 20A radials, to get even 32A let alone 40A it has to be correctly split between the circuits, which the customer knows nothing about and may not be convenient. E.g. if a room gets flooded and needs drying out, they will plug two heaters and a dehumidifer in there and the 32A circuit would be OK with that, whereas a 20A might trip. I know that's an unusual situation but there are lots of similar scenarios.

This is one of the advantages of the 32A socket outlet circuit that is often overlooked - a larger circuit with more points makes better use of diversity and is less likely to get overloaded if the loads are not in the anticipated places. A typical family home with GCH will run quite happily on a single 32A circuit. Not ideal in the event of a fault etc. but it works fine for loading. Our entire living area used to run fine on one 30A Wylex MCB with lounge, dining room and kitchen including washing machine, tumble dryer, dishwasher, fridge, freezer, microwave etc. Theoretically you can't put just the washer and dryer together on a 20A.

But, importantly, the distinction between 32A circuits and 20A circuits is a different one to the difference between RFC's and radials. The current rating dictates how many circuits are needed, the RFC / radial aspect dictates cable size, testing method etc. A 32A radial provides the same functionality as a 32A RFC.
 
I agree with all of that. But of course, a 32A radial needs more copper than a 32A RFC.

On overloading radials, at a local church the boiler broke down so they had to use electric heaters - which could barely take the chill off. Of course, someone got over ambitious - and after blowing a fuse (radial on 15A rewirable fuse), told me he'd been careful and plugged them into different sockets :rolleyes: He was also amazed that I was able to find the blown fuse :astonished:
 
I rarely do final ring circuits now, generally radial in 4mm but watch the cable length.
 
I cannot understand how someone can be working on electrics in Canada and not know the voltage is 120v plus or minus 5%. 110v is a myth and outside the permitted tolerance.

I can't understand how you can tell from his post that he was working on the 120V public supply and not a 110V supply for special purposes. Considering the kind of installations Pete has told us he worked on either is clearly possible.
 
Hi all,

This may be a common topic and may already have been spoken about 100s of times so forgive me in advance.

I have always wired in ring mains for my sockets up until recently..

I came across an install where all sockets were wired in 2.5 radials protected by 20A RCBO they had wired 3 bedrooms all on separate 2.5 radials (Loft & 1st floor)
i did question why each room was separate and the response i got was "customers request due to computers"

I am hearing more and more people wiring 4mm radials protected by 32A as its "convenient"

whats peoples general thoughts on this?
As long as the 4mm2 Radial complies with 433/1 and Appendix 15 BS7671 I see no problems at all with a Radial wired in 4mm2 protected by either a 30A or 32 A OCPD
 
I came across an install where all sockets were wired in 2.5 radials protected by 20A RCBO they had wired 3 bedrooms all on separate 2.5 radials (Loft & 1st floor)
i did question why each room was separate and the response i got was "customers request due to computers"
IMO there's a lot to be said for this sort of arrangement - as well as reasons against. It does mean that if one offspring trips the RCD using damaged hair curlers, it doesn't "cause family discord" by tripping off the power to another offspring's gaming rig in the next room, or to dad's servers ;) OK, someone could potentially overload a circuit by plugging in (eg) two fan heaters, kettle's, whatever - but that's just going to trip the overload protection and not damage the wiring, and it's not exactly likely in most homes.
It's going to cost more in RCBOs, but they are coming down nicely in price these days so not likely to be a deal killer as part of the grand scheme.

At our last house I was considering splitting the (single) RFC into two radials - in part because of the difficulty of doing stuff room by room while maintaining the integrity of the ring and not having non-compliant spurs. Haven't determined what to do with the current house yet ...

A an aside, I've seen a new and quite small office wired with what seemed like a ridiculous number of RFCs for the same "because, computers" reason. A couple of jobs (and more years than I care to work out :rolleyes:) ago when I first came across this, I went and measured the earth leakage of a representative sample of our IT kit and found ... nothing significant, definitely no reason to be talking about only using single sockets, high integrity earthing arrangements, and so on.
 
IMO there's a lot to be said for this sort of arrangement - as well as reasons against. It does mean that if one offspring trips the RCD using damaged hair curlers, it doesn't "cause family discord" by tripping off the power to another offspring's gaming rig in the next room, or to dad's servers ;) OK, someone could potentially overload a circuit by plugging in (eg) two fan heaters, kettle's, whatever - but that's just going to trip the overload protection and not damage the wiring, and it's not exactly likely in most homes.
It's going to cost more in RCBOs, but they are coming down nicely in price these days so not likely to be a deal killer as part of the grand scheme.

At our last house I was considering splitting the (single) RFC into two radials - in part because of the difficulty of doing stuff room by room while maintaining the integrity of the ring and not having non-compliant spurs. Haven't determined what to do with the current house yet ...

A an aside, I've seen a new and quite small office wired with what seemed like a ridiculous number of RFCs for the same "because, computers" reason. A couple of jobs (and more years than I care to work out :rolleyes:) ago when I first came across this, I went and measured the earth leakage of a representative sample of our IT kit and found ... nothing significant, definitely no reason to be talking about only using single sockets, high integrity earthing arrangements, and so on.
our house, built c.1956 was rewired by my lady's dad in the 80's. being Polish, he did not understand rings, so 2 radial socket circuits wired into a 30A HRC fuse which originally fed a RFC. otherwise, a good install. new CU (fitted my my good self) split socket circuits on to 2 x 20A MCBs. now have the benefit if separation of circuits, RCD protected (except for the garage/man cave with the freezers and workbench)). risk assessment in my addled brain.
 
As I've said, I don't know, but it's not beyond possibility. As far as I know the reverse is also true for US government installations in non US countries, they have 120V 60Hz supplies.
Dave, just to add credence to the argument, George seems to be bent on perpetuating, please see below. Some relevant information for you, as if you weren't aware of it already, I was there the voltage was measured at 110 60 Hz we had a Stabiliser at our intake set at a steady state of 110V 60 Hz backed up by a UPs built for us by UK company, no expense spared. Say no more.
 
Last edited:

Reply to Radials V Ring mains in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all I would like to put some sockets in the attic and keep them on the main house ring main. Am I right in saying I can pull one of the legs...
Replies
1
Views
200
Essentially I have a "normal" socket in a ring mains, i.e. one 2.5mm T&E going in and one 2.5mm T&E going out. I am looking to simply add two more...
Replies
2
Views
287
HI All, I am building a new house (self build) and have my part P so am running the cabling. My reading of the regs says that any appliance of...
Replies
18
Views
4K
Hello, Last year I had some electrical work completed in my house (New CU, SWA for garage, downlights) I informed the electrician that I will be...
Replies
8
Views
2K
Hello Electrical world. Looking for thoughts and opinions. Currently planning out my kitchen re-wire for new kitchen. I was originally...
Replies
13
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock