Discuss Random voltage/Power loss in the The Welcome Forum area at ElectriciansForums.net

Shorne

-
Reaction score
1
Hello everyone I am a new member to this and was wondering if anyone can help.

We have a client at a pub that randomly loses power to several circuits for about 2 seconds, then comes back on. We are trying to establish whether the problem is coming from the incoming supply or a sub circuit. The electrical suppliers are saying that the problem is not on the incoming supply , is there any tests I can do to establish why and where they are having this?

Thanks
 
first your visual tests. check all terminations applicable to the suspect circuit/s. then it's logical sequence of dead testing followed by live testing, as in the book/s.
 
The problem is that it's not just one final circuit that loses power, its several and its random.

Also the problem is coming from 2 separate fuseboards. We have done visual checks. We originally found one fuseboard had internal busbar damage which we have since replaced but the problem still persists.

It's so random that they could go days without anything happening.
 
The problem is that it's not just one final circuit that loses power, its several and its random.

Also the problem is coming from 2 separate fuseboards. We have done visual checks. We originally found one fuseboard had internal busbar damage which we have since replaced but the problem still persists.

It's so random that they could go days without anything happening.

Is it just random circuits or a whole Dis board that drops out ?.
 
I think the clue is "at a pub" - pubs are notorious for carp electrical installations..... best get some more facts..... but the basic checks on live and neutral connections would make sense........
 
If the faults are that random then a voltage logger won't do much good, what circuits would you connect to ?

As Murdoch said, pub wiring is notorious. Especially if a brewery in house job.
 
Last edited by a moderator:
I'm thinking of putting voltage logger at main incomer i.e supply side of main switch to see if any issues at source. Asked UKPN to come out to set this up but that could be other side of Christmas
 
The problem is that it's not just one final circuit that loses power, its several and its random.

Also the problem is coming from 2 separate fuseboards. We have done visual checks. We originally found one fuseboard had internal busbar damage which we have since replaced but the problem still persists.

It's so random that they could go days without anything happening.

Sorry just re read this, are you saying that after changing 1 board the problems still exist on that board ?
 
I'm thinking of putting voltage logger at main incomer i.e supply side of main switch to see if any issues at source. Asked UKPN to come out to set this up but that could be other side of Christmas

Sorry mate: Maybe I'm getting dense with age, but how would that help ? If it was a supply problem then all circuits on that board would drop out not one or two random circuits.
 

Reply to Random voltage/Power loss in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

90s house electric issues continues 🥲 So after getting some good advice here I've managed to sort out some of the heating issues so thank you...
Replies
2
Views
235
Hello, I’ve got an issue driving me crazy and can’t get anyone to figure it out as it’s not their issue. We had a new extension, single rear...
Replies
9
Views
1K
Hi everyone, I'm a newbie to the forum, and I'm hoping my question won't be too stupid. I'm in NYC (Manhattan), and have an apartment where a...
Replies
3
Views
546
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
867
Hi, The `power went out throughout the house this afternoon but only to the sockets, the lighting circuits are all fine. I went to the consumer...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock