Hi,
I visited a property suffering from random tripping of the 100ma RCD. I found several very loose terminals in the CU neutral and CPC screws. I tightened those and the problem disappeared for a couple of days. Originally it was happening every couple of hours.
This morning I get a call saying it has reoccurred.
The CU has all circuits except lights on a 30ma RCD and three lighting circuits on the 100ma RCD side (main switch).
The 30ma RCD never trips.
I have tested Zs and IR readings for all circuits and all fine with IR above 200. RCD Trip times are also ok but ramp test on the 30ma side was 15 ma before tightening screws and 18ma after.
Also neither RCD will turn back on until ALL MCBs are off.
Any suggestions from previous similar problems?