Hi,

I visited a property suffering from random tripping of the 100ma RCD. I found several very loose terminals in the CU neutral and CPC screws. I tightened those and the problem disappeared for a couple of days. Originally it was happening every couple of hours.

This morning I get a call saying it has reoccurred.

The CU has all circuits except lights on a 30ma RCD and three lighting circuits on the 100ma RCD side (main switch).

The 30ma RCD never trips.

I have tested Zs and IR readings for all circuits and all fine with IR above 200. RCD Trip times are also ok but ramp test on the 30ma side was 15 ma before tightening screws and 18ma after.

Also neither RCD will turn back on until ALL MCBs are off.

Any suggestions from previous similar problems?
 
Surely got to be one of the lighting circuits at fault though - probably a case of trying to work out what was on at time of tripping and trying to find the pattern. Any external lights that might be coming on with pir?
 
Full insulation resistance test of the lighting circuits, being sure to switch all switches. Is there any outside lighting? Sensor controlled lights etc?
 
The RCD is an 80A 100ma standard type (not time delayed).

The tripping started again today when the house was empty and no lights were on, they turned it back on, went out again and same again. It as two PIR lights which are in a covered area but it is tripping in the day so the PIR is not activating.
 

Reply to Randon RCD tripping in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
346
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
829
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Keeping this brief.....................New dwelling.....TT system with 100mA S type rcd protected supply to local board with 30mA RCD. Freelance...
Replies
21
Views
3K
Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
816

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock