Discuss Rangemaster Cooker Load in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
Hello Guys

Looking for some advice with regards to a extension job. Customer has ordered a Rangemaster Induction Hob and Oven.

I've looked at the specification and it states that potential full load is 14.8Kw. My initial plan was to run a 10mm Twin and Earth but I'm wondering if it would potentially need a 16mm. I understand diversity applies to cooker circuits and its full load will likely not be ever used but was looking for a bit of advice. Would 16mm supply cable be over kill.


Thanks
 
Diversity will apply. Have a read of the chapter in the OSG on max demand and diversity. From that, you should be able to calculate a design current for the circuit, and from there be able to design your circuit. Also have a look at manufacturer's instructions regarding maximum conductor sizes, suggested protective device etc.
 
Diversity will apply. Have a read of the chapter in the OSG on max demand and diversity. From that, you should be able to calculate a design current for the circuit, and from there be able to design your circuit. Also have a look at manufacturer's instructions regarding maximum conductor sizes, suggested protective device etc.
I've just checked the manufacturers installation booklet again
Diversity will apply. Have a read of the chapter in the OSG on max demand and diversity. From that, you should be able to calculate a design current for the circuit, and from there be able to design your circuit. Also have a look at manufacturer's instructions regarding maximum conductor sizes, suggested protective device etc.
I've just checked the manufacturers Instruction and it states a 45Amp Fuse Rating. Nothing about size of conductor but a 10mm should be suffice on a 50amp RCBO.

Cheers for the pointer👍
 
I've just checked the manufacturers installation booklet again

I've just checked the manufacturers Instruction and it states a 45Amp Fuse Rating. Nothing about size of conductor but a 10mm should be suffice on a 50amp RCBO.

Cheers for the pointer👍
Done a quick calculation as per Page 122 of OSG and it should pull in 27 Amps with Diversity applied.
 

Reply to Rangemaster Cooker Load in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, We have an old Country villa in Spain. The housing electrics were not good so the house recently has been completely re-wired to a good...
Replies
2
Views
741
Hello everyone, I'd like to seek your input on a matter. I'm in the process of designing the electrical connections for the following kitchen...
Replies
38
Views
3K
Hi, during kitchen refurbishment, the electrician installed a 4mm cable and 32a breaker for the new induction hob rangemaster oven that is rated...
Replies
44
Views
8K
Hello. New member here. Electrical enthusiast. I am at a friend's house in the Bahamas and decided to look at the load center in the house, which...
Replies
2
Views
414
Hello, Looking at changing out my gas hob for the PIV851FB1E Bosch Induction Hob. The Induction hob is 7400W and by my calculations this would...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock