I am an adult learner. I understand the theory behind the 30mA trip rating (for example) of an RCD but I need some help understanding what the 63A rating (for example) actually means. My understanding is that RCD's do not provide over current protection, that would be provided by MCBs (for example) downstream of the RCD. Am I correct in saying that the 63A rating (for example) is the "switching" rating of the device rather than the current carrying capacity of the device? Any advice would be appreciated.
 
It is the maximum continuous current that can be passed through it.

it will be capable of disconnecting under full load but will not provide any over current protection
 
  • Like
Reactions: DPG
It is the maximum continuous current that can be passed through it.

it will be capable of disconnecting under full load but will not provide any over current protection
Thank you for your prompt reply. I watched a video from a well respected YouTube electrician (bigclive.com) and he was tearing down an RCD that was sent in by an electrician to see whether overload was the cause of failure. (View: https://www.youtube.com/watch?v=9wcPw5hUNpQ
) and he shows a picture of the CU that it was removed from. He also says that "..the 63A isn't a tripping current, it's the current it can handle on a continuous basis" (As you say above). I attach an image from the video and can't understand what an electrician would set up a CU with such high loads all (on a split board) 1 RCD. Any thoughts would be appreciatedto_forum.jpg
 

Reply to Rating of RCD's in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

I was wondering if someone might be able to help either confirm or change my understanding on the use of S-Type RCDs. I believe that they can be...
Replies
1
Views
662
Ok, most new Consumer unit seem to come with a 63A RCCB and two MCBs. Most house consumer units now will also have RCD of some type be it a dual...
Replies
24
Views
1K
My circuit panel has two banks of breakers, each bank protected by an RCD. One of these RCDs has been problematic in that it trips intermitantly...
Replies
12
Views
1K
Hi, Because of the recent epidemics of so called experts with absolutely no proper qualification, nor knowledge, I'm forced to learn more on the...
Replies
4
Views
833
Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
804

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock