tomasi

Would normally expect when wiring ring mains
nowadays for data serving equipment to use high integrity
earthing.
Is the following true:
If the following applies you don't have to do it:

1.Use of a Rcbo as long as the Rcbo is 30ma rated
and the earth leakage current expected will not be
greater than 25% of the Rcbo rated trip current.

2.Limit the number of outlets to a minimum on the ring
when knowing the number to use when knowing the earth leakage at each point.

----------------
Can earth leakage from other circuits say high
frequency lighting create a hazard to other circuits
Should high frequency lighting circuits be questioned
to see if they require high integrity earthing.
 
Yes I understand that high integrity earthing is based upon the assumption that a larger conductor would have
a greater mechanical reliability as would 2 individual conductors connected to 2 individual terminals at every
point they utilize.
Also duplicate conductors of which one maybe suitable steel conduit or the like.
I only pose the original question as a devils advocate.
 
Last edited by a moderator:

Reply to Rcbo and high integrity earthing cop out in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

2nd fixing some sockets in an office today and we were talking about high integrity earthing, I've not got a clue what the sockets are going to...
Replies
9
Views
1K
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
752
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock