Discuss rcbo functional earth in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

tank

-
Reaction score
16
hello, does the functional earth of a rcbo have value of loop impedance that has to be met in order for it to work as designed?
 
i was curious as to whether having a ze of say 156 Ω on a tt system as opposed to say 0.2 Ω on a tncs would have any effect on the operation of the fe on a rcbo
 
None! The functional earth is used by the RCBO as reference for the internal electronics necessary to increase the sensitivity and speed of operation needed to miniaturise the earth fault functionality and package it in a one module unit not much bigger than MCB. It also allows the device to detect an earth fault, even if in a rare event of the neutral becoming disconnected.
 

Reply to rcbo functional earth in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi just wondering if someone can help me. I have an rcbo that keeps tripping but only when the fly earth and neutral lead on the bars it trips...
Replies
10
Views
387
So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Replies
3
Views
1K
Anyone know of an RCBO manufacturer, apart from Chint,that includes an indicator in the RCBO to indicate if the trip is a earth fault or an overload.
Replies
2
Views
749
Folks. I need to install a defib unit outside on a wall. Does this require an RCBO or not, just wondering as the unit has a small heater within...
Replies
15
Views
533
Hi All I'm new here. I have just finished my NVQ and waiting to do my AM2. I have a question on selectivity as it has always slightly confused me...
Replies
5
Views
797

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock