Hi guys I have a client whos rcbo keeps tripping, never when I am there and at all times day and night.i have stripped circuit down insulation readings all over 200meg ramp test on rcbo is 21ma . should this be higher or is it ok thanks paul
 
is a bit low. 21mA . swap the RCBO and see if it cures the problem.
 
Ok lets cut to the chase what is it supplying ie a ring, a radial an immersion a cooker ? more infor is required plus your ramp test did you disconnect the circuit ?
 
ramp it first with all loads disconnected..(you`v done this already)...
then ramp it again with all loads connected....
the difference is leakage....
I would be changing that RCBO n all....
but confirm the leakage present first wont you...
i`v told you how to do it...
 
I had this situation with one of my clients on a rewire I did.
there is 2 options (which worked for me)
1. offer to PAT Test all appliances within the property
2. Tell them to keep a record of what is plugged in (turned on or off) when the RCBO tripped - or tell them just to call you as soon as it trips and not to touch anything - not even turn it back on!
 
A wander lead is a handy piece of kit and so is a nice long extension lead.
These 'trips' are trial and error and testing will show zilch a lot of the times.

As the guys have already said..............there are always 'prime suspects' so......................

Plug your nice long extension cable into another cct ( upstairs ring?) then plug in the prime suspect ( freezer?) and see if the rcbo still trips..............etc etc until you find the culprit:)
 

Reply to rcbo leakage tripping in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
Ring main was on a c40 rcbo so I tested the circuit everything was fine and dropped down onto a b32, It’s quite a long circuit but only serves...
Replies
26
Views
2K
I have a ring cct (2.5mm ) in my cabin which is protected by a 20amp RCBO. This has been in existence for over 3 years with no issues. I recently...
Replies
18
Views
1K
I have an issue with a home lighting circuit 6A RCBO provides power to 13 bulbs which randomly keeps tripping, when I say randomly it keeps...
Replies
8
Views
2K
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
732

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock