Yes, not very good design but equally not dangerous.

The Zs is higher than UK regs on OCPD alone but given your 32A C-curve trip range for 230V covers Zs = 1.1*230/(5*32) = 1.58 ohms best-case down to 0.8 * 0.95 * 230 / (10 * 32) = 0.54 ohms worst-case, your measured 0.83 is going to be met for over half the tolerance range, and the RCD side always met.
 
Agree, with the Rcd in circuit, R1+R2 tests, its compliant not ideal but ok.
The worry I have these days is that the lesser experience electricians, we’ve a high Zs reading put a Rcd on it.
Without the relevant tests it’s a major concern, days gone by you would certainly fix the problem
 
Agree, with the Rcd in circuit, R1+R2 tests, its compliant not ideal but ok.
The worry I have these days is that the lesser experience electricians, we’ve a high Zs reading put a Rcd on it.
Without the relevant tests it’s a major concern, days gone by you would certainly fix the problem
Exactly, if it is just a rather long cable then it is not so serious, even though it is probably not meeting the VD spec either. But it could be something more serious that ought to be fixed (bad joint, etc) and not simply side-stepped with the RCD aspect.
 
Thank you all so much for the replies
And sorry for late response I'm working away at the moment and haven't had much time or that good internet connection I had noted on cert that it was a poor design and there is a few other issues I am due to go back and rectify once I am working back local thanks again the collective hive mind
 

Reply to Rcbo with higher than permitted zs in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, I did my first EICR on a TT system today and the Zs was a lot higher than Ze+R1+R2 on everything. Zs was around 3.5 ohms on all of the ring...
Replies
10
Views
1K
OLDBOY
O
Ring main was on a c40 rcbo so I tested the circuit everything was fine and dropped down onto a b32, It’s quite a long circuit but only serves...
Replies
26
Views
2K
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
497
As a retired electrician, I need to specify a new type B board for a village church. Principal load is heating. Ipfc phase to phase is 1.1kA...
Replies
10
Views
1K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock