Discuss Rcbo in the UK Electrical Forum area at ElectriciansForums.net

Pete999

-
Esteemed
Arms
Reaction score
17,092
I should know the answer but I don't and have tried google etc so that's out of the way for starters. Reading a post about sockets used for IT equipment and the possible problems caused by RCD tripping due to start up earth leakage, led to think about protecting the circuit with RCBOs with a time delay, problem is I'm not sure if there is such an animal, at least I have never come across one. Question is do they exist?
 
I should know the answer but I don't and have tried google etc so that's out of the way for starters. Reading a post about sockets used for IT equipment and the possible problems caused by RCD tripping due to start up earth leakage, led to think about protecting the circuit with RCBOs with a time delay, problem is I'm not sure if there is such an animal, at least I have never come across one. Question is do they exist?


I use small 16a rcbo radial circuits to prevent the possibility of this, rather than 32a ring circuits
 
The problem with using a time delay RCD is that they cannot be used as additional protection because the time delay means that you cannot meet the 40 ms disconnection at 5Idn, and since the reason for applying the RCD protection to sockets circuits is for additional protection this precludes time delay.

I believe someone once found a 30mA time delay RCD but I cannot fathom when it would be useful to use one as 100mA would be more appropriate.
 
The problem with using a time delay RCD is that they cannot be used as additional protection because the time delay means that you cannot meet the 40 ms disconnection at 5Idn, and since the reason for applying the RCD protection to sockets circuits is for additional protection this precludes time delay.

I believe someone once found a 30mA time delay RCD but I cannot fathom when it would be useful to use one as 100mA would be more appropriate.


Thanks Mate
 

Reply to Rcbo in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

hi all come across a new build commercial office where radial circuits feeding electrak power track was protected by 32A RCBO at dist board and...
Replies
15
Views
1K
I’m probably going to look stupid here, but it will be worth it if I get the answer 😆, as I can’t fathom it out. I’ve never really thought of it...
Replies
22
Views
733
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
732
I have an issue with a home lighting circuit 6A RCBO provides power to 13 bulbs which randomly keeps tripping, when I say randomly it keeps...
Replies
8
Views
2K
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
915

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock