Hi I have a 6 way split load board located in the shed and served by 10mm SWA. Anything on the unprotected side of the board tests and works fine. However this is not the same for the protected side. I can plug a radio in and the circuit does not trip, but if I use the lawn mower or a drill the RCD trips immediately. In addition, the RCD does not trip when the test button is pushed. I have swapped out the RCD too. Nothing trips on the house board when the RCD in shed trips. All connections are secure in CU. Any ideas where to go next?
 
If the RCD is wired correctly plus there's power to it and it doesn't trip on the test button then replace it again, no if's or but's, it's faulty. The tripping under load could be a crossed/borrowed neutral or an insulation fault or it could also be a symptom of a faulty RCD.

Replace it then do global IR testing and recheck neutrals.
 
Thanks for the reply (mean or not) :) . I didn't fit the board, we just moved in. The board looks like an off the shelf pre fitted one.
 
I have had this happen with the neutrals being crossed over to a different neutral bar. Id check that first and also treble check the wiring on all protected circuits but as Marvo says, if its wired correctly and the trip button doesnt activate then the RCD is faulty...
 
Hi Jabbajaws. I have removed all circuits from the board and fitted a single socket and it still trips. I will check the neutrals. Would crossed neutrals cause the RCD not to trip on test?
 
Hi Murdoch, looking at it, the swa comes from a protected circuit on the main house cu. This runs 150' to the end of the garden into the 6 way. SWA is earthed at house CU.
 
Hi Jabbajaws. I have removed all circuits from the board and fitted a single socket and it still trips. I will check the neutrals. Would crossed neutrals cause the RCD not to trip on test?
One Neutral should come from the bottom of the Main switch into the first neutral bar, then from that neutral bar into the top of the RCD, then from the bottom of the RCD into the second neutral bar.
 
that's not the problem, but it's bad design as a fault on the sub-main circuits can cause the house RCD to trip, thus losing part of the house installation. i have had a similar fault caused by a N-E reversal in back of a socket outlet.
 
that's not the problem, but it's bad design as a fault on the sub-main circuits can cause the house RCD to trip, thus losing part of the house installation. i have had a similar fault caused by a N-E reversal in back of a socket outlet.
I can move the load to an unprotected side of the board.
 
that would eliminate the series RCDs. i think you need to look more closely at the garage installation for a fault once you have determined that you have a good RCD.
 

Reply to RCD doesnt trip on test. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
349
What should you do if a client has a CU that is a split board protected by 2 * 63Amp 30mA double pole RCCDs, you took Zs and tested both RCCDs by...
Replies
22
Views
2K
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
2K
Hi, I swapped a 2 gang switched socket for a 2 gang switchless socket with usb ports downstairs. I switched off all the power to the house by...
Replies
8
Views
788
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock