Discuss RCD for car chargers and zappi install in the UK Electrical Forum area at ElectriciansForums.net

Steve93

-
Trainee
Reaction score
15
where does every one source there Rcd’s from for car chargers? I know you need the types A etc but where actually has these on the shelf? Or at least next day?

Also has anyone got finished install pics of the zappi charger?
Thanks in advance
 
best supplier believe it or not is rolec. any usual wholesaler such as denmans, rexel group and its various names.
Yes they are rebadged chint but they are readily available and reasonably priced. coincidentally fit into chint enclosures! otherwise if you want others i would look at online suppliers.
I have not fitted a zappi unit but they should all have integral rcd protection. if you are protecting the outgoing circuit you can normally feed it off a standard rcbo or mcb/rcd set up. the dc protection is largely done at charger end. depending on method you may still want to rcd protect the supply cable but then have to think about discrimination or selectivity as we have to say now.
i just checked the zappi manual online and it says feed it using a mcb. the charger has integrated rcd protection for the ac and dc protection required.
https://myenergi.uk/wp-content/uploads/2017/10/zappi-manual-v1.2.pdf
 
Thank you for your reply!
You have a very good point there I do see rcd not Necessary.
It will be in its own d.b and swa clipped direct. So an mcb should be sufficient.
Depending on Earth arrangement for TT I guess?
 
Thank you for your reply!
You have a very good point there I do see rcd not Necessary.
It will be in its own d.b and swa clipped direct. So an mcb should be sufficient.
Depending on Earth arrangement for TT I guess?
We wont get into the debate about pme and whether it is suitable following risk assessment or whether the supply is tns back to the station.
Just put it on a rod and be done with it, if you struggle getting one in, get a ground rod driver off ebay and use the sds. the things go in much easier then! come 18th they will all be on rods anyways.

out of interest, are you in a competent persons scheme? as ev chargers are notifiable to both the dno and building control under the part p criteria.
 
Yes I’ve done the EV C&G course. My problem is that it’s going next to solar inverters outside that are on the house earthing arrangement. I haven’t got my cop book on me to look it up but I’m sure if there is a different earthing arrangement that can be touched between the car and inverter (which there is) measures need to be taken? What’s your views?
 
IMG_20180902_112948.jpg IMG_20180902_112936.jpg
This one has 8M lead attached..
 

Reply to RCD for car chargers and zappi install in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
Hi all, been reading around this and i have to admit ive quickly gone out of my depth as regards EV chargers. The charger in question is a...
Replies
18
Views
2K
Hi Everyone, before I start ill admit I have very little knowledge of EV chargers etc, I have had a question from a customer who has had a 7kw...
Replies
13
Views
3K
Hi, sorry if this has already been discussed or is in the wrong place. Im wondering if anyone has come across a domestic EV charger where the ct...
Replies
1
Views
549
I am an NICEIC contractor but I have never installed an Electric vehicle charger. I have watched all of the relevant NICEIC webinars (The wire) on...
Replies
18
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock