Discuss RCD keeps Tripping, need some Advice in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
My RCD began to trip several months ago. I narrowed it down to a fridge/freezer in the garage. However, after turning this off, its now started to trip again due to another fridge/freezer (in the last few weeks). Either I’m incredibly unlucky and both appliances need replacing, or there’s something more sinister causing it to trip. Not sure whether to buy new ones or whether the RCD unit or something else is to blame?
 
Sounds like you are just incredibly unlucky, if after unplugging the second fridge/freezer the tripping problem has been resolved.
You could get the appliances and RCD tested but my feeling is it will just confirm what you already know.
 
It could be a N-E fault, and it is triggered by the compressor kicking in. So any large load would do the same as it causes enough of a volt drop on the neutral so sufficient current is diverted via the earth/CPC for the RCD to notice, and the fault may not be on the circuit you think is causing it if the RCD is also feeding a few other circuits.

If you have anything else with a large-ish motor that starts directly, say an old vacuum cleaner (not one with a soft-start electronic control) you could see if that does the same thing at that socket.

An electrician could run an IR test for such a fault, also they ought to be able to check for obvious faults on the appliance (the "PAT testing" sort of check). They also can test the RCD trip times and ramp-test to see what leakage current it actually trips at.

Replacing things "just in case" can be a more frustrating and expensive approach than methodical testing!
 
How often does the RCD trip if it is every 24 - 48 hours then I would suspect an auto defrost heater element fault on the fridge freezer
 
It could be a N-E fault, and it is triggered by the compressor kicking in. So any large load would do the same as it causes enough of a volt drop on the neutral so sufficient current is diverted via the earth/CPC for the RCD to notice, and the fault may not be on the circuit you think is causing it if the RCD is also feeding a few other circuits.

If you have anything else with a large-ish motor that starts directly, say an old vacuum cleaner (not one with a soft-start electronic control) you could see if that does the same thing at that socket.

An electrician could run an IR test for such a fault, also they ought to be able to check for obvious faults on the appliance (the "PAT testing" sort of check). They also can test the RCD trip times and ramp-test to see what leakage current it actually trips at.

Replacing things "just in case" can be a more frustrating and expensive approach than methodical testing!
This! Totally unrelated N-E fault is much more likely than two similarly faulty fridge freezers.
What other circuits are fed by this RCD?
 
In most situations like this it's less that 2 hours work for a decent sparks to identify what is going on. That would be considerably less than replacing the appliance again.
However, after turning this off, its now started to trip again due to another fridge/freezer (in the last few weeks)
You said "after turning this off". To ask a silly question, is it still plugged into the wall with the switch off?
 
It could be a N-E fault, and it is triggered by the compressor kicking in. So any large load would do the same as it causes enough of a volt drop on the neutral so sufficient current is diverted via the earth/CPC for the RCD to notice, and the fault may not be on the circuit you think is causing it if the RCD is also feeding a few other circuits.

If you have anything else with a large-ish motor that starts directly, say an old vacuum cleaner (not one with a soft-start electronic control) you could see if that does the same thing at that socket.

An electrician could run an IR test for such a fault, also they ought to be able to check for obvious faults on the appliance (the "PAT testing" sort of check). They also can test the RCD trip times and ramp-test to see what leakage current it actually trips at.

Replacing things "just in case" can be a more frustrating and expensive approach than methodical testing!
Typically happened most in the middle of the night (so was easier to assume freezer compressor), but on other occasions it’s just been quite random (definitely not when using another large compliance).
 
In most situations like this it's less that 2 hours work for a decent sparks to identify what is going on. That would be considerably less than replacing the appliance again.

You said "after turning this off". To ask a silly question, is it still plugged into the wall with the switch off?
Yes, plug in but switched off. Does that make a difference?
 
How often does the RCD trip if it is every 24 - 48 hours then I would suspect an auto defrost heater element fault on the fridge freezer
Mainly at night, but has also done this on other occasions. With both fridge/freezers off it’s not happened since. Small fridge still works, but now without a freezer :(
 
This! Totally unrelated N-E fault is much more likely than two similarly faulty fridge freezers.
What other circuits are fed by this RCD?
The RCD covers mainly an area that was part of an extension the previous owners did to create a utility room. So sockets, some lights, outside lights, immersion. On the sockets we have the washing machine, dryer, x2 fridge/freezers (utility and in garage). Most of the time it happened at night. I’ve attached photo of fuse box / RCD.
 

Attachments

  • E6E34EE5-D749-47F8-9199-7999A4221B93.jpeg
    446.8 KB · Views: 13

Reply to RCD keeps Tripping, need some Advice in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I am asking for help as a novice and 1st time user of this forum. Recently started to experience tripping of MCB & sometimes with the RCD at...
Replies
7
Views
584
Hi, I moved home a few months ago and the electrics RCD keep tripping. Sometimes it will happen every few days and sometimes will be fine for a...
Replies
86
Views
7K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock