Discuss RCD / LED problem in the Commercial Electrical Advice area at ElectriciansForums.net

Next time don't give the customer the option.

They are running as business ... Hours lost cost far more than a couple of rcbo's

Best get back on site and use your tester
 
You are absolutely right about not giving a customer an option in this case.

I will be there next week and try to get an earth leakage metre too. They are not cheap but seem very useful.
 
The clamp is a must,on issues such as this,but if the only thing i had was a screwdriver,i would be pulling the neutral on that mcb switched lighting circuit,and seeing what happened...
 
Theoretically the LEDs cannot be affecting the RCD on a different supply as the RCD is only monitoring the outgoing circuits.
Possibly, but I am not sure how, the LED dimmer is introducing a DC component that is masking the RCD operation; alternatively if there is a Neutral Earth fault on the sunbed side of such resistance that is just tripping the RCD and there is also a neutral earth fault on the LEDs once switched on then this would give parallel paths for the neutral current and so reduce the current seen by the RCD below its tripping threshold.
If the sunbeds are switched on by a double pole switch then it is possible that there is a difference in arcing across the poles so that the RCD occasionally thinks there is an imbalance and the LEDs just happen to coincide with the trip times. This could be tested by connecting the "working" sunbed to one of the other sockets.
 
So when the LEDs are on, the RCD doesn't trip? All one one RCD?
If so it could simply be the sun beds are leaking inductively to earth and the LEDs are leaking capacitively. So they cancel out enough to stop a trip. Not sure how well RCD trip if you leak imaginary power, but either way the above suggestions about one 3p RCD per bed make sense.
 
So when the LEDs are on, the RCD doesn't trip? All one one RCD?
If so it could simply be the sun beds are leaking inductively to earth and the LEDs are leaking capacitively. So they cancel out enough to stop a trip. Not sure how well RCD trip if you leak imaginary power, but either way the above suggestions about one 3p RCD per bed make sense.
Did you test the RCD?
Did you test the RCD with the LEDs on or off?
 
Hi - The shop's LED lights with no functional switch caught my eye - an indicator perhaps the rest of the place isn't wired as we might expect?

I was wondering this but he has stated the new rcd board is wired independently of the existing cu which supplies the led light circuit ......

Very odd

Hope we get feedback once he’s been back on site ..
 
http://www.solansunbeds.co.uk/How_to_Set_up_a_Successful_Tanning_Salonv1.2.pdf

See page 16 of 17 of the reference which is quite clear that if RCD protection is provided for Solan sunbeds then the trip current difference must be 100mA and not 30mA to take into account the accumulated leakage from the many ballasts and hot humid ambient air inside the equipment. What do the technical installation instructions say for the make and model of tanning machine for which you have provided electrical supplies?
 
Gives a good insight as to why RCBO should be used for each one. Hopefully 30mA rating will be ok, as I'm not overjoyed at the idea of stepping in and out of a metal box with 100mA ... (is it just me?) Still no clue as to the LED role in all this :) .
 

Reply to RCD / LED problem in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi Guys I've fitted a few emergency lighting circuits to both domestic and commercial installs before, I've come across one I can't get my head...
Replies
19
Views
1K
I was wondering if someone might be able to help either confirm or change my understanding on the use of S-Type RCDs. I believe that they can be...
Replies
1
Views
667
Morning guys, I would like some advice, currently at my workplace, I am replacing a DB and existing wiring in a warehouse. One of the ways feeds...
Replies
4
Views
1K
Good morning, I'm in the process of a partial refurbishment which will involve the present kitchen being changed into a bedroom instead and the...
Replies
3
Views
938
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
911

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock