Discuss RCD problem in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

R

rlz

Hi
When I do a loop test on an installation protected with an rcd using my robin kmp 4118 (no d lock) the rcd doesnt trip.
Both the tester and rcd have been tested ok by other means - any ideas?
Thanks
A very frustrated engineer
 
Agree with Mark on that.

Some manufacturers RCD's or RCBO's wont trip when loop testing.

If they do trip, then the only option normally is to bridge out the RCD temporarily.
 
Agree with Mark on that.

Some manufacturers RCD's or RCBO's wont trip when loop testing.

If they do trip, then the only option normally is to bridge out the RCD temporarily.


RCDs aren't supposed to be bridged out, if the RCD trips the value should be calculated using
Zs=Ze+R1+R2 and then noted on the test sheet
 
As long as you are confident the RCD AND the Loop tester are functioning correctly then I cant see any problem.
As the above post states Zs can be obtained by calculation ,and in fact in some cases to prevent Live Working... this is the only acceptable method to use.

spark1
 

Reply to RCD problem in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
781
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
What should you do if a client has a CU that is a split board protected by 2 * 63Amp 30mA double pole RCCDs, you took Zs and tested both RCCDs by...
Replies
22
Views
2K
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
Keeping this brief.....................New dwelling.....TT system with 100mA S type rcd protected supply to local board with 30mA RCD. Freelance...
Replies
21
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock