- Reaction score
- 10
Providing 10kva 400v/110v transformers on site and not sure if i need to protect the SWA feeding the TX with RCD.
Comments please.
Comments please.
Discuss Rcd Protection For Supply To A Transformer On Construction Site? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Providing 10kva 400v/110v transformers on site and not sure if i need to protect the SWA feeding the TX with RCD.
Comments please.
So how did you pass the 2391 then?thanks, i was really after knowing the exact details, i e, L on L1 N on L2 and E on e.....at socket and then press test, as ive only ever plugged in the plug to the socket and pressed test.
What do you think people used before RCDs were invented?
You can if the tncs supply is supplying a fixed building on the construction site 704.411.3.1you do know that you can't use a tn-cs supply for a construction site I hope.
Reply to Rcd Protection For Supply To A Transformer On Construction Site? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net