Currently reading:
RCD protection on multiple 3 phase machines

Discuss RCD protection on multiple 3 phase machines in the UK Electrical Forum area at ElectriciansForums.net

D

Dave 85

Hi guys

Just wanted to pick your brains on the following...
I've been doing some work in a Jaguar dealership and they've had a health and safety guy come around and recommend that all existing socket circuits and 3 phase car ramps should be given RCD protection. I have been asked to quote for said work.

Now we are looking at 10 3phase ramps and around 12 socket circuits fed from 4 different DB's (old brown square D ones) which are all 20 odd meters apart.

Ideally I wanted to replace at least 3 of the DB's so I could put RCBO protection on all socket circuits but I'm not sure what to do with the ramps....as far as I'm aware you cant get 3phase RCBO's??? and having an RCD main switch on each board seems like a very poor option.

One though is to replace the DB's, keep MCB's on the ramps but then install remote RCD isolators for each ramp. Obviously I'm trying to make this cost effective.

Any advice would be much appreciated.

Thanks
 
If only the workers of the factory are using the ramps and sockets then there is no need to add RCD's. I'll find the reg.
 
Are the non electrical workers(fitters) classed as competent users of electrical equipment? Brings out the old debate about competency? I'd argue not and RCD protection would be beneficial? But that's my opinion?
As for the lift, you need to refer to the installation methods etc
 
Are the non electrical workers(fitters) classed as competent users of electrical equipment? Brings out the old debate about competency? I'd argue not and RCD protection would be beneficial? But that's my opinion?
As for the lift, you need to refer to the installation methods etc

It's Skilled or Instructed not competent.
A cleaner can be classed as Skilled or Instructed.

Yes RCD would still be beneficial tho.
 
Last edited:
If H&S want RCD then they won't settle for less regs or no regs.

Well if they insist then let them have the RCD's. You can point out that according to reg 411.3.3 its not really needed as the workers should be classed as either skilled or instructed.
 
First thing I would do, is find out what happens if you loose power to the lifts, does it drop?

What you could do is mount the 3 phase RCD's in adaptable boxes at the point where the ramp is plugged into the socket, and wire the RCD's into the sockets.
 
Well if they insist then let them have the RCD's. You can point out that according to reg 411.3.3 its not really needed as the workers should be classed as either skilled or instructed.

Thanks Spoon. This did occur to me when discussing it and I did point out to them that RCD's in commercial premises were somewhat of a grey area. On the other hand if they insist on having the work done then I am happy to do it for them.
I may have to go back and do a bit of further investigation before quoting. I didn't for example, check weather the ramps take a neutral or just 3 phases.
It does make me laugh how these so called 'health and safety experts' can walk around wielding the power to make decisions well beyond their obviously limited knowledge.
 
First thing I would do, is find out what happens if you loose power to the lifts, does it drop?

What you could do is mount the 3 phase RCD's in adaptable boxes at the point where the ramp is plugged into the socket, and wire the RCD's into the sockets.

So in a power cut all mechanics get crushed under their work hhhhmmm.. think that won't be the case!
 
Thanks Spoon. This did occur to me when discussing it and I did point out to them that RCD's in commercial premises were somewhat of a grey area. On the other hand if they insist on having the work done then I am happy to do it for them.
I may have to go back and do a bit of further investigation before quoting. I didn't for example, check weather the ramps take a neutral or just 3 phases.
It does make me laugh how these so called 'health and safety experts' can walk around wielding the power to make decisions well beyond their obviously limited knowledge.

Anytime mate. As snowhead has said pointed out, H&S may insist, so just fit them. Some of the H&S people are ok but some just love the power that they have.
 
431.3.3 - note1
314.1(iv)
531.2.4

If the ramps are routinely serviced and are supplied via a fixed outlet not a plug/socket affair then their is no need for rcd protection, if however the ramps are portable and the run 400v flexes across the workshop floor then the socket outlets require rcd protection IMHO... if the motors on the ramps are VFD controlled then the above regulations will be contravened and alternative methods of powering the units need finding so flexes dont run across workshop.

The H&S quangos are a law unto themselves and unless you state throwing relevant reasons and regulations at them they dont want to know .... id also put to them that all cost incurred due to nuisance tripping of RCD's will be passed to them as they are stipulating measures beyond BS7671..... if they agree to anything you put forward ask for it in writing too as an amendment to their original wishes.
 
Sockets I can understand RCD’s. Surely the ramps are fixed, it just doesn’t make any sense.

Im not saying RCD's are a bad thing here. Even with the sockets, the factory workers should only be using them for tools that they have been trained to use.. Just my opinion..
 
id also put to them that all cost incurred due to nuisance tripping of RCD's will be passed to them as they are stipulating measures beyond BS7671..... if they agree to anything you put forward ask for it in writing too as an amendment to their original wishes.

That will make them think twice..
 
I wasn't having a go at you, just the whole idea of RCD everything.

Sorry Tony. I know you wasnt having a go at me.... Its just the way I word things, it always comes across as aggressive... and im a little ----- cat really...
 
Is everyone missing the obvious here, run the supply in armoured to each ramp, and to previous posters, no the ramps don't drop hen the power is disconnected there are latching mechanism in place for just that.


What about 4 post portable rigs with trailer plug supply.... this is a case where i would have the supply covered just been to a garage and the S/Y extension lead 3ph/400v (Yes i know i took them out of service immediately) went across the workshop and was both damaged and had lost its earth.... the OP hasn't expressed the set-up but in general for fixed set-ups i see no need for rcd cover also most newer ramps have selv control power and only have LV to motor which is usually mechanically protected ... Also to note here is only the supply to the ramp is covered by the BS7671 the ramp itself isn't.
 
and mustn't forget the full face protection in cookery class when mixing things like tea and water.
 
I dont see the point to be honest.
We recently had a similar issue but we said the staff who would be working with the equipment in question would be part of the engineering dept and therefore did not need the rcd protection.

However where we have had to rcd protect the 3 phase gear for whatever reason we have brought 3 phase socket outlets with built in rcbo's.
 
I just want to be a fly on the wall and see the expression on the H&S persons face when Dave goes along with darkwoods post 15, and states that he will add the RCD's when he receives a written demand for them from H&S and "all cost incurred due to nuisance tripping of RCD's will be passed to them as they are stipulating measures beyond BS7671"
 

Reply to RCD protection on multiple 3 phase machines in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top