hi guys if a bank of 20 sockets wired in surface trunking on a radial circuit,these sockets would be used for computers gameboys and music equipment,my question is would they need to be rcd protected ? i know normally they would not,it's just that my mate said if protecting computers they should, i cannot find anything on this
 
hi guys if a bank of 20 sockets wired in surface trunking on a radial circuit,these sockets would be used for computers gameboys and music equipment,my question is would they need to be rcd protected ? i know normally they would not,it's just that my mate said if protecting computers they should, i cannot find anything on this
If the said socket outlet circuit is subject to high earth leakage current then the circuit needs to be wired differently than a normal Ring FC or Radial FC as per Regulation 543.7.1.201 information can be found on page 81 OSG and Figures 7.5.3 (1) and 7.5.3 (11) Page 82 OSG
 
If the said socket outlet circuit is subject to high earth leakage current then the circuit needs to be wired differently than a normal Ring FC or Radial FC as per Regulation 543.7.1.201 information can be found on page 81 OSG and Figures 7.5.3 (1) and 7.5.3 (11) Page 82 OSG
i would be running a separate earth along with dual earth terminals just cannot see anything regarding rcd
 
to omit RCD protection for these sockets, you would have to do a written risk assessment justifying a reason why. what's to stop someone plugging in a faulty appliance?
 
to omit RCD protection for these sockets, you would have to do a written risk assessment justifying a reason why. what's to stop someone plugging in a faulty appliance?
these sockets are for my friend and will be solely for computer and stereo equipment and not for outdoor purposes etc
 
411.3.3 Additional protection requirements for socket-outlets and for the supply of mobile equipment for use outdoors
In AC systems, additional protection by means of an RCD with a rated residual operating current not exceeding 30mA shall be provided for:
(i)socket-outlets with a rated current not exceeding 32A, and
(ii)mobile equipment with a current rating not exceeding 32A for use outdoors.
An exception to (i) is permitted where, other than for an installation in a dwelling, a documented risk assessment determines that RCD protection is not necessary.
 

Reply to rcd protection on sockets in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

hi all come across a new build commercial office where radial circuits feeding electrak power track was protected by 32A RCBO at dist board and...
Replies
15
Views
1K
Essentially I have a "normal" socket in a ring mains, i.e. one 2.5mm T&E going in and one 2.5mm T&E going out. I am looking to simply add two more...
Replies
2
Views
307
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
933
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
570
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
774

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock