happysteve

-
Esteemed
Arms
Supporter
Reaction score
2,115
Doing standard tests prior to some minor works on a socket circuit (Zs, IR etc), pressed the test button on the RCD, tripped fine, got ready to measure trip times but the RCD would not reset. Tiny bit of resistance as you first start lifting the lever, then goes completely floppy, i.e. you can lift the lever but it's not engaging with anything, and doesn't hold. Tried a few times but would not reset.

Disconnect the N out of the RCD, (all downstream circuits already turned off), and this time the RCD reset. "Ah!" I thought, "Maybe some pretty serious N-E fault is preventing me resetting it!" So like a fool I pressed the test button again - it tripped - and then wouldn't reset. Tried turning off the main switch - no difference, still won't reset.

So off I go to the van, to see if I've got something that fits well enough before I can get a matched replacement by the same manufacturer. By the time I come back from the van, I can reset the RCD.

At this point, I figure it just needs a little rest before being reset. Sure enough, I managed to do all the standard RCD tests, all disconnection times were well within spec, it just needed 2-3 minutes after tripping each time before it could be reset.

It is a Contactum B6303/2: BS EN 61008, 2-pole, 63A, 30mA, type AC.

Anyone experienced anything similar?
 
Sounds like it is a "feature" of that design. To me it is a fault but if that is really the way they behave then I guess it is a pass. Just a tedious test to verify that.
 
There are a pair of those RCDs not ten feet from where I'm sitting and never had any issue with resetting after pressing the test switch. Replaced one after about a year, when it became overly sensitive and progressively more difficult to reset after each trip.
 

Reply to RCD requires a little rest before resetting in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
331
Doing a kitchen job for my daughter’s music teacher, who also happens to have been in my wife’s class at school. Nothing big… just a little...
Replies
2
Views
244
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock