Discuss RCD test button not working in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Hi guys I'm an amateur but I have the same problem. Can you explain what you mean by an N-E fault (an earth cable on the neutral and vice versa?) Also if I swich of each MCB one by one and try the test button would that identify which circuit the fault was on? I won't fix it myself but I like to understand what's happening and where.
 
First of all, there is a very low resistance between the earth and neutral wires where they enter your property. If you have a TNC-S (PME) earthing system, they are actually connected directly together at the service head.
If there is a short circuit or bad leakage between the earth and neutral wires anywhere in your property, some of the current flowing normally in the neutral wire on an unrelated circuit anywhere else in the property will find its way through this N-E fault, back through the earth wire to the service head, and then flow into the incoming neutral, so bypassing the N side of the RCD, while the full current is passing through the L side.
Very difficult to diagnose without the correct equipment, but hopefully should become a problem of the past, as RCBOs which switch both N and L (far from all do at the moment) become more common.
 
Yes, appliances can be equally responsible.
 
So unplugging all appliances and retrying the test button might be a good first step - or the house has 11 mcbs might turning them off one and trying the test button by one identify a duff (technical word) circuit?
 
Turning off normal single-pole (SP) MCBs won't narrow it down, as they don't switch the neutrals. Hence Brian's comment that over time, with the increasing use of RCBOs with double-pole switching that do isolate the neutrals, troubleshooting will get easier.
 
Thank you.
So can this be caused by an appliance that is plugged in and has a fault?
And turned off at the socket, in most cases. Some sockets have double pole switching, but they are rare.
This is something I've spent hours on the 'phone, trying to explain customers, while trying to avoid being dragged out on 'emergency' calls.
 
Thank you - but what if it hasn't been pressed for say 3 years - I am just buying a socket tester with a "RCD test button" I will try this on a circuit to see if that trips the MCB (I assume that "safely" shorts the live and earth) I will explain the "3 Years later!"
 
If a RCD isn't tested regularly, the hair trip mechanism can become stuck in place and the contacts of the test button can tarnish. If you can get it to trip, and then 'exercise' the mechanism, by tripping and resetting it several times, they can usually be brought back to life.
Note that anon working test button is a fail when an electrical condition report (EICR) is undertaken, and will result in the installation being declared 'unsatisfactory'.
 
Thanks for all your advice I really appreciate it - so trying to trip the MCB via a socket tester would show if the problem was with the test button and if the RCD was working or not?
Now I will explain the three years - The Consumer unit is in Thailand! and was installed by a "professional" electrician (at least as professional as you will get in Thailand when we built the house - EICR in Thailand -non existent) 8 years ago.
I tested the RCD at least twice a year until - Covid struck and I was in the UK and my Thai partner was in Thailand we were apart for just over 2 years and asking her to check it would have been a useless exercise and I must admit when I got back in January I forgot to check it until now!
 
Your socket tester is better than nothing, in that it will confirm that the RCD is kaput, if it is, but a full test involves checking that it trips within a certain range of leakage current, and measuring the time it takes to disconnect the power, which has an upper limit.
 
Your socket tester is better than nothing, in that it will confirm that the RCD is kaput, if it is, but a full test involves checking that it trips within a certain range of leakage current, and measuring the time it takes to disconnect the power, which has an upper limit.
I understand what you are telling me and of course if I find I need to replace it I will get a "professional" to do that.
This is the tester I am buying - I'll let you know and thanks again
 

Attachments

  • Screenshot 2022-12-17 105612.png
    389.3 KB · Views: 11
Sorry to bother you again but I have just noticed that the RCD in my consumer unit has a variable trip can be set to 5, 10, 20, 30 (currently 20) and the socket tester is available in 30 Ma or 5 Ma RCD tester should I buy the 5 Ma socket tester not the 30 Ma tester as being more sensitive?
 
The 30ma tester should trip it. Being set at 20ma anything above this which 30ma is should cause it to trip.
 

Reply to RCD test button not working in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

What should you do if a client has a CU that is a split board protected by 2 * 63Amp 30mA double pole RCCDs, you took Zs and tested both RCCDs by...
Replies
22
Views
2K
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
331
Hi, I swapped a 2 gang switched socket for a 2 gang switchless socket with usb ports downstairs. I switched off all the power to the house by...
Replies
8
Views
781
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
I'm not an electrician. I clean cookers and today arrived to a rangemaster range cooker. Got started, and as part of my routine, I turn on ovens...
Replies
1
Views
751

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock