Discuss Rcd test in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Rcd Test Procedure

Many RCD test meters have a facility where tests can be carried out during the positive or negative half of the supply cycle.

For tests 1 & 2 the RCD operating time to be recorded is the longer of the two measured during the half cycle tests.

Do not press the test button on the RCD before testing as this can temporarily reset a faulty RCD.

Test 1
Adjust the current setting on the test meter to 100% of the rated trip current of the RCD and perform a test. A general purpose BS4293 RCD should operate within 200ms. A general purpose BS61008 RCD or RCBO to BS61009 should operate within 300ms.

Test 2
An RCD provided for basic protection should have a rated trip current not exceeding 30ma. If the RCD is rated at 30ma, adjust the current setting on the test meter to 150ma (x5) and perform a test. The RCD must operate in a time not exceeding 40ms.

Test 3
Adjust the current setting on the test meter to 50% of the RCD trip current and perform a test. The RCD should not operate within 2 seconds.

The Test Button
Finally operate the RCD by pressing its test button.
 
cj are you training to be an electrician. If so what stage are yot at? I was shown the different testers and what they were for very soon after starting. Maybe you should ask your employer to do the same. But someone did give you a full and brilliant answer above. Plus it is known as a megger not a megga. That is not the instrument for an rcd test tho.
 
Good idea Phil,

And also make sure you hit the thanks button MANY times.

Amberleaf has given more information in those threads than i think most of us have together.

And all for nothing.
 
The other option is handy man tips, a bit of a you tube star, sure he will have a section on testing, How do you test for a live circuit? as Pevvers would probably say......With a wet finger........
 
just as a matter of course, this is a very helpful forum with some great guys who know there stuff.
its not however a replacement for real training as an electrician.
i would suggest buying a book (Gn3) or similar
 
hi can anybody tell me the exact correct procedure for testing the BS EN 60309-2 three phase socket on an RCD test for the 2391 much appreciated
 

Reply to Rcd test in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
344
Hi I am asking for help as a novice and 1st time user of this forum. Recently started to experience tripping of MCB & sometimes with the RCD at...
Replies
7
Views
561
I was wondering if someone might be able to help either confirm or change my understanding on the use of S-Type RCDs. I believe that they can be...
Replies
1
Views
662
Hi All DALI lighting system distributes circuit via LCM's, for electrical test, do you stop at the LCM or light point. how do you carry out...
Replies
2
Views
395
I recently just done my AM2 resit and in my inspection and testing, despite the invigilator watching me do the tests, I think I may have forgotten...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock